If you're asking me Chris, quite the contrary. It seems that everyone else
is saying bracing only applies where performance per ASCE 7 is required,
whereas I think the 40/80 tuff applies for everything except in seismic
zones where more severe requirements apply.

On Thu, Mar 14, 2013 at 7:03 PM, Cahill, Christopher
<[email protected]>wrote:

> Are you thinking sway bracing of mains and large BL's 9.3.5 vs. restraint
> of BL's 9.3.6?  Only applies when seismic is required 9.3.
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For
> *Registered in: MN
>
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, March 14, 2013 8:57 PM
> To: [email protected]
> Subject: Re: Seismic and ASCE 7
>
> Doesn't 13 require sway bracing on all systems and seismic bracing, per
> the prescriptive methods of 13 that meet the performance criteria of ASCE 7
> or by engineering calculations per that same criteria, when in a seismic
> zone that requires seismic bracing. Now that was a mouthful but sway
> bracing and seismic bracing are very distinct things in my mind. But then I
> may be misinterpreting.
>
> On Thu, Mar 14, 2013 at 6:42 PM, Chris Born <[email protected]> wrote:
>
> > My opinion is that sprinkler systems are not required to be braced
> > under ASCE 7 in seismic design category B.  ASCE 7 specifically
> > exempts mechanical and electrical equipment in seismic design category
> > B.  I believe it appropriate to consider a sprinkler system under the
> > same umbrella as mechanical and electrical systems.
> >
> > Mechanical and electrical systems are also exempt from seismic
> > protection in seismic design category C, unless the importance factor
> > is greater than 1.  Because sprinkler systems have an importance
> > factor of 1.5, they do require seismic protection in design category C.
> >
> >
> > Christopher Born, P.E.
> > Director, Fire Protection Engineering
> > Clark Nexsen
> > Norfolk, VA
> >
> > Sent from my iPad
> >
> > On Mar 14, 2013, at 6:03 PM, "Bob" <[email protected]> wrote:
> >
> > > There is a project that I am not involved in, but the AHJ called for
> > > an opinion.  The situation revolves around the idea that if a
> > > building is in site class C and design category B, the sway bracing
> > > requirements of
> > NFPA 13
> > > are waved by ASCE 7.  I have not come across this before, and there
> > > is a certain fire sprinkler contractor that is eliminating the sway
> > > bracing, retaining straps, etc... on several large warehouse /
> > > distribution buildings.  The claim is that ASCE 7 allows for this.
> > > Has anyone come across this and have information verifying or
> > > negating it?  I am meeting with several AHJ's in regard to this
> > > tomorrow morning, so any input will
> > be
> > > extremely useful.
> > >
> > > Thank you,
> > >
> > > Bob Knight, CET III
> > > 208-318-3057
> > > www.firebyknight.com
> > >
> > >
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130314/a75973cc/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130314/d49cf496/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to