A question on topic for a change. Is it necessary for the rod to touch the top 
of 2.5" branch lines with less than 6" from the top of pipe to the attachment? 
The verbage seems to say yes but the diagrams show the end of rod not touching 
the pipe.

Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, March 15, 2013 7:06 AM
To: [email protected]
Subject: RE: Seismic and ASCE 7

In a perfect world, my friend.  I lost my perspective of reality for a minute 
there.  Sorry.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, March 15, 2013 9:31 AM
To: [email protected]
Subject: RE: Seismic and ASCE 7

What "fire protection engineered drawings"? I wish I had a dollar for every 
time the "FP Consultants" on a project (when there is one) told me that we are 
responsible for meeting code and that we are the EOR. The projects with no 
consultant go much smoother for us because there is no confusion. If we ask 
about hose valves at the horizontal exits because none were shown on the 
standpipe schematic they furnished, they tell us they aren't the EOR and we are 
responsible for complying with code.

Ron F 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, March 15, 2013 5:40 AM
To: [email protected]
Subject: RE: Seismic and ASCE 7

A couple of years back we had a company come in and do their dog and pony show 
regarding seismic bracing for mechanical systems.  They specialize in the 
hardware but also will do the engineering and provide a complete package to the 
contractor for installation.

SDC A & B as has been stated in this discussion, do not require bracing on 
sprinkler systems.  SDC C is when it begins and those requirements can be met 
by applying the prescribed methods within NFPA 13.  When you get to SDC D then 
special engineering and special inspections come into play.

Please don't talk about Seismic Zones as they were once shown in NFPA 13, those 
zones are not relevant anymore and are not used to determine the need for 
seismic bracing.

Lastly, the info regarding the need for EQ bracing should be on the fire 
protection engineered drawings.  This should not be left up to the sprinkler 
contractor to determine.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to