Yes - Tank serves sprinklers and hydrants

NFPA 13 2010 edition

Figure 11.2.3.1.1       .20/1500

Table 11.2.3.1.2                250 hose for 60 minutes min (assume remote 
supervision)


Jack W. Carlson, SET
Triple "A" Fire Protection
Office - 251.649.2034
Fax - 251.649.2037
Cell - 706.247.5050

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby 
Gillett
Sent: Monday, May 13, 2013 1:19 PM
To: [email protected]
Subject: Sizing tanks with hydrants?

When sizing a water storage tank feeding a fire pump for a new facility with 
multiple sprinkler systems and fire hydrants, do you have to include any type 
of allowance for the hydrants? The tank will be the sole source of supply for 
all (rural area). There will be no hose stations or standpipes, only interior 
sprinkler systems - OH Group II with monitored alarms.
Typically this would be an 18,000 gallon tank minimum (.20x1500x60 mins). I 
don't see anywhere that requires this, just making sure.

 

Thank you in advance.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 