The building will never be used for high piled storage right? 

Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
Gillett
Sent: Monday, May 13, 2013 1:19 PM
To: [email protected]
Subject: Sizing tanks with hydrants?

When sizing a water storage tank feeding a fire pump for a new facility with
multiple sprinkler systems and fire hydrants, do you have to include any
type of allowance for the hydrants? The tank will be the sole source of
supply for all (rural area). There will be no hose stations or standpipes,
only interior sprinkler systems - OH Group II with monitored alarms.
Typically this would be an 18,000 gallon tank minimum (.20x1500x60 mins). I
don't see anywhere that requires this, just making sure.

 

Thank you in advance.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 