Forgot this one: 

NFPA 1:18.4.5.2.1   Required fire flow shall be reduced by 75 percent when the 
building is protected throughout by an approved automatic sprinkler system. The 
resulting fire flow shall not be less than 1000 gpm (3785 L/min).

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C] 
Sent: Monday, May 13, 2013 2:10 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

NFPA 1:18.4.1* Scope.  

A.18.4.1   Section 18.4 and the associated tables are only applicable for 
determining minimum water supplies for manual fire suppression efforts. Water 
supplies for fire protection systems are not addressed by this section. It is 
not the intent to add the minimum fire protection water supplies, such as for a 
fire sprinkler system, to the minimum fire flow for manual fire suppression 
purposes required by this section.

>From the Handbook:

The explanatory material in A.18.4.1 clarifies that the intent of the Code is 
not to add the fire flow calculated in accordance with Section 18.4 to an 
automatic sprinkler system demand. For sprinklered buildings, the required 
water supply should be the greater of either that specified by Section 18.4 or 
the demand for the automatic sprinkler system. Section 18.4 is used to 
calculate the required fire flow for manual fire-fighting purposes and does not 
take into account fire suppression systems or hose stream requirements required 
by other codes and standards, such as NFPA 13, Standard for the Installation of 
Sprinkler Systems. Fire protection system water supply requirements are not 
permitted to take advantage of the reduction in fire flow in 18.4.5.

If you are in a rural area, see also NFPA 1142. There is another method to 
calculate the required water supply...

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services National 
Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"

-----Original Message-----
From: Bobby Gillett [mailto:[email protected]]
Sent: Monday, May 13, 2013 2:04 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

No. This is a tech school. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Art
Tiroly
Sent: Monday, May 13, 2013 12:48 PM
To: [email protected]
Subject: RE: Sizing tanks with hydrants?

The building will never be used for high piled storage right? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
Gillett
Sent: Monday, May 13, 2013 1:19 PM
To: [email protected]
Subject: Sizing tanks with hydrants?

When sizing a water storage tank feeding a fire pump for a new facility with
multiple sprinkler systems and fire hydrants, do you have to include any
type of allowance for the hydrants? The tank will be the sole source of
supply for all (rural area). There will be no hose stations or standpipes,
only interior sprinkler systems - OH Group II with monitored alarms.
Typically this would be an 18,000 gallon tank minimum (.20x1500x60 mins). I
don't see anywhere that requires this, just making sure.

 

Thank you in advance.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <http://www.keyfireprotection.com> www.keyfireprotection.com

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2241 / Virus Database: 3162/5820 - Release Date: 05/13/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3336 / Virus Database: 3162/6313 - Release Date: 05/10/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________