Couldn't you just put the pressure gauge on the flange connection before
the hose valve?  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Todd - Work
Sent: Wednesday, June 19, 2013 6:28 AM
To: [email protected]
Subject: water test without hydrants

I have a client who tapped a new 6"  line into an 8" public main which
does not have any hydrants on it. Now we have to get a flow test. My
thought is to put a flange on the 6" with a 2-1/2" hose valve, to which
I connect my fire hose and Hose Monster. We would then need to find a
nearby property tapped off that line and read pressures from that
system. It seems to make sense, but am I missing something?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com