It is a matter of where you want the test to be "effective".  If you really 
want to know what the public supply can provide, then thestatic and residual 
readings need to be taken off of that main.  In Phoenix I used to use the 
upstream tap on the  nearest backflow prevention assembly, but in Phoenix, 
these were at the property line, above ground, because we did not worry about 
freezing conditions.  I have used hose bibs at properties, after ensuring that 
there were not check valves between the bib and the water supply.

Regards,

Dwight




________________________________
 From: Todd - Work <[email protected]>
To: "[email protected]" 
<[email protected]> 
Sent: Wednesday, June 19, 2013 8:21 AM
Subject: Re: water test without hydrants
 

Wouldn't that be the equivalent of putting the pressure gauge on another outlet 
of teh flow hydrant?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On Jun 19, 2013, at 8:08 AM, "Martinez, Dewayne" 
<[email protected]> wrote:

> Couldn't you just put the pressure gauge on the flange connection before
> the hose valve?  
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Todd - Work
> Sent: Wednesday, June 19, 2013 6:28 AM
> To: [email protected]
> Subject: water test without hydrants
> 
> I have a client who tapped a new 6"  line into an 8" public main which
> does not have any hydrants on it. Now we have to get a flow test. My
> thought is to put a flange on the 6" with a 2-1/2" hose valve, to which
> I connect my fire hose and Hose Monster. We would then need to find a
> nearby property tapped off that line and read pressures from that
> system. It seems to make sense, but am I missing something?
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to