How far back is the nearest set of fire hydrants?  If needed, flow test the 
closest hydrants, review the as-built plans for the underground water mains and 
include all of pipe, fittings and elevation changes in the hydraulic 
calculations.

Dan Failla
Charleston Fire Marshal's Office
Charleston SC

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd - Work
Sent: Wednesday, June 19, 2013 7:28 AM
To: [email protected]
Subject: water test without hydrants

I have a client who tapped a new 6"  line into an 8" public main which does not 
have any hydrants on it. Now we have to get a flow test. My thought is to put a 
flange on the 6" with a 2-1/2" hose valve, to which I connect my fire hose and 
Hose Monster. We would then need to find a nearby property tapped off that line 
and read pressures from that system. It seems to make sense, but am I missing 
something?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com