This may vary by state. We've done engineered stand-alone booths, but they
were located in a rated room where paint is also stored and mixed. The
question was about a framed compartment - the rest is the architect's
issue.

Steve

"[email protected]" <[email protected]> wrote:

Is this a K-12 school, or a community college. Adult education usually
defaults to a B-occupancy, then goes to special occupancies or uses. If it
is a high school it should be an E-occupancy.

Spraying in an E-occupancy normally requires a paint spray room. Booths
are not an option in E occupancies. See IFC 2404.2, IBC, IMC, and adopted
electrical code.

Was the booth installed under benefit of permit?

bv

----- Original Message -----
From: "Steve Leyton" <[email protected]>
To: [email protected]
Sent: Friday, July 26, 2013 12:14:37 PM
Subject: RE: Paint booth

Not sure there's a recognized 90 minute assembly. There are one and two
hour, but I think the architect would have a hard time gaining approval
for a 90 minute assembly without an appeal or approval of alternative
means and methods of construction. For this type of booth (we've done 3 in
high schools recently) the industry standard for pre manufactured is
either one or two hour.

Steve

"J.P. Merlino" <[email protected]> wrote:

Can the room design method be applied provided the walls of the room in
which the paint booth is located, are 90 min fire rated ?

If the room is under 2500 sq ft it will make a big difference in the water
supply and storage.

J.P. Merlino

-----Mensaje original-----
De: [email protected]
[mailto:[email protected]] En nombre de Steve
Leyton
Enviado el: viernes, 26 de julio de 2013 02:10 p.m.
Para: [email protected];
[email protected]
Asunto: RE: Paint booth

Yes, but if it's not rated I would say you need to do a design for EH II
that encompasses the booth, the mixing room, and adjacent spaces (assuming
no 2-hour separations from adjacent uses) up to the required design area
in
11.2.3.1.1.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [email protected] on behalf of Douglas
Hicks
Sent: Fri 7/26/2013 10:09 AM
To: [email protected]
Subject: Paint booth

I have been asked by a local school district about protecting an
automotive
paint booth. The catch, the booth is 2 x 4 framed, covered with sheet
rock.
The exhaust duct work does not have filters, and the exhaust fan may not
be
rated for hazardous paint fumes. The booth does not meet any UL
standards,
so I cannot install a dry chemical suppression system. Will a water
based
sprinkler work?
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg


-----
No se encontraron virus en este mensaje.
Comprobado por AVG - www.avg.com
Version: 2013.0.2904 / Base de datos de virus: 3209/6522 - Fecha de
publicacion: 07/26/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to