Charles, Ron, this is off topic. I can beat the story about the cardboard box. There is a resturant here in Eastern Oregon, I serviced the Ansul once. The Ansul defiencies bothered me enough so I would not do the service again. The hood was made of alumiminum and single wall duct, not grease tight. A few years later, a class reunion was held in the resturant. We went, and I noticed the exhaust hood and appliances were gone! The kitchen was moved into the back room. I went over and peaked in the back room and there was a new hood over the appliances. I was disappointed to see the new exhaust hood was not protected by a fire suppression system. But the lack of a suppression system was not the real problem. The hood did not meet any UL, NFPA or IMC standards. It was made of cardboard! Yes, the hood was made of cardboard. The duct tape that held the cardboard to the wall and the duct probably did not meet code either. But, they did not have to worry about grease build-up in the hood, they just replaced the cardboard box.

You just cannot make this stuff up!

-----Original Message----- From: Charles Thurston
Sent: Sunday, July 28, 2013 10:57 AM
To: Ron Greenman
Subject: Re: Paint booth

Hello Ron,

Actually happened in a body shop here after the city inspector told them they needed "Sprinklers" in the spray booth (non sprinkled building) 3/8" poly from the saddle tap under the water cooler ran 50' across the building, Then split to the 2 heads in the spray booth. City inspector "approved" their installation 5-6 years ago and is still like that.

Sunday, July 28, 2013, 11:03:49 AM, you wrote:

so just
increase that to a really big pipe like 1" after tapping the line that goes
to the water cooler.


On Sun, Jul 28, 2013 at 12:55 AM, Douglas Hicks <[email protected]> wrote:

Hi School, Sophomore to Senior
Permit?  Not a chance, No Way.  Does that cost more?
This is the third sheet rock booth I have seen.  None were permitted or
inspected.
-----Original Message----- From: [email protected]
Sent: Friday, July 26, 2013 5:30 PM
To: sprinklerforum@lists.**firesprinkler.org<[email protected]>
Subject: Re: Paint booth

Is this a K-12 school, or a community college. Adult education usually
defaults to a B-occupancy, then goes to special occupancies or uses. If it
is a high school it should be an E-occupancy.

Spraying in an E-occupancy normally requires a paint spray room. Booths
are not an option in E occupancies. See IFC 2404.2, IBC, IMC, and adopted
electrical code.

Was the booth installed under benefit of permit?

bv

----- Original Message -----
From: "Steve Leyton" <[email protected]>
To: sprinklerforum@lists.**firesprinkler.org<[email protected]>
Sent: Friday, July 26, 2013 12:14:37 PM
Subject: RE: Paint booth

Not sure there's a recognized 90 minute assembly. There are one and two
hour, but I think the architect would have a hard time gaining approval
for a 90 minute assembly without an appeal or approval of alternative
means and methods of construction. For this type of booth (we've done 3 in
high schools recently) the industry standard for pre manufactured is
either one or two hour.

Steve

"J.P. Merlino" <[email protected]> wrote:

Can the room design method be applied provided the walls of the room in
which the paint booth is located, are 90 min fire rated ?

If the room is under 2500 sq ft it will make a big difference in the water
supply and storage.

J.P. Merlino

-----Mensaje original----- De: sprinklerforum-bounces@lists.**
firesprinkler.org <[email protected]>
[mailto:sprinklerforum-**[email protected].**org<[email protected]>]
En nombre de Steve
Leyton
Enviado el: viernes, 26 de julio de 2013 02:10 p.m.
Para: sprinklerforum@lists.**firesprinkler.org<[email protected]>
;
sprinklerforum@lists.**firesprinkler.org<[email protected]>
Asunto: RE: Paint booth

Yes, but if it's not rated I would say you need to do a design for EH II
that encompasses the booth, the mixing room, and adjacent spaces (assuming
no 2-hour separations from adjacent uses) up to the required design area
in
11.2.3.1.1.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message----- From: sprinklerforum-bounces@lists.**
firesprinkler.org <[email protected]> on
behalf of Douglas
Hicks
Sent: Fri 7/26/2013 10:09 AM
To: sprinklerforum@lists.**firesprinkler.org<[email protected]>
Subject: Paint booth

I have been asked by a local school district about protecting an
automotive
paint booth. The catch, the booth is 2 x 4 framed, covered with sheet
rock.
The exhaust duct work does not have filters, and the exhaust fan may not
be
rated for hazardous paint fumes. The booth does not meet any UL
standards,
so I cannot install a dry chemical suppression system. Will a water
based
sprinkler work?
______________________________**_________________
Sprinklerforum mailing list
Sprinklerforum@lists.**firesprinkler.org<[email protected]>
http://lists.firesprinkler.**org/listinfo.cgi/**
sprinklerforum-firesprinkler.o<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o>
rg

______________________________**_________________
Sprinklerforum mailing list
Sprinklerforum@lists.**firesprinkler.org<[email protected]>
http://lists.firesprinkler.**org/listinfo.cgi/**
sprinklerforum-firesprinkler.o<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o>
rg


----- No se encontraron virus en este mensaje.
Comprobado por AVG - www.avg.com
Version: 2013.0.2904 / Base de datos de virus: 3209/6522 - Fecha de
publicacion: 07/26/13

______________________________**_________________
Sprinklerforum mailing list
Sprinklerforum@lists.**firesprinkler.org<[email protected]>
http://lists.firesprinkler.**org/listinfo.cgi/**
sprinklerforum-firesprinkler.o<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o>
rg

______________________________**_________________
Sprinklerforum mailing list
Sprinklerforum@lists.**firesprinkler.org<[email protected]>
http://lists.firesprinkler.**org/listinfo.cgi/**
sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
______________________________**_________________
Sprinklerforum mailing list
Sprinklerforum@lists.**firesprinkler.org<[email protected]>
http://lists.firesprinkler.**org/listinfo.cgi/**
sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
______________________________**_________________
Sprinklerforum mailing list
Sprinklerforum@lists.**firesprinkler.org<[email protected]>
http://lists.firesprinkler.**org/listinfo.cgi/**
sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>







--
Best regards,
Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to