That was good, Douglas.

On Sun, Jul 28, 2013 at 4:45 PM, Douglas Hicks <[email protected]> wrote:

> Charles, Ron, this is off topic.  I can beat the story about the cardboard
> box.  There is a resturant here in Eastern Oregon,   I serviced the Ansul
> once.  The Ansul defiencies bothered me enough so I would not do the
> service again. The hood was made of alumiminum and single wall duct, not
> grease tight.  A few years later, a class reunion was held in the
> resturant.  We went, and I noticed the exhaust hood and appliances were
> gone!  The kitchen was moved into the back room.  I went over and peaked in
> the back room and there was a new hood over the appliances.  I was
> disappointed to see the new exhaust hood was not protected by a fire
> suppression system.  But the lack of a suppression system was not the real
> problem.  The hood did not meet any UL, NFPA or IMC standards.  It was made
> of cardboard!    Yes, the hood was made of cardboard.  The duct tape that
> held the cardboard to the wall and the duct probably did not meet code
> either.  But, they did not have to worry about grease build-up in the hood,
> they just replaced the cardboard box.
>
> You just cannot make this stuff up!
>
> -----Original Message----- From: Charles Thurston
> Sent: Sunday, July 28, 2013 10:57 AM
> To: Ron Greenman
> Subject: Re: Paint booth
>
> Hello Ron,
>
> Actually happened in a body shop here after the city inspector told them
> they needed "Sprinklers" in the spray booth (non sprinkled building) 3/8"
> poly from the saddle tap under the water cooler ran 50' across the
> building, Then split to the 2 heads in the spray booth. City inspector
> "approved" their installation 5-6 years ago and is still like that.
>
>
> Sunday, July 28, 2013, 11:03:49 AM, you wrote:
>
>  so just
>> increase that to a really big pipe like 1" after tapping the line that
>> goes
>> to the water cooler.
>>
>
>
>  On Sun, Jul 28, 2013 at 12:55 AM, Douglas Hicks <[email protected]> wrote:
>>
>
>  Hi School, Sophomore to Senior
>>> Permit?  Not a chance, No Way.  Does that cost more?
>>> This is the third sheet rock booth I have seen.  None were permitted or
>>> inspected.
>>> -----Original Message----- From: [email protected]
>>> Sent: Friday, July 26, 2013 5:30 PM
>>> To: sprinklerforum@lists.**firespr**inkler.org<http://firesprinkler.org>
>>> <sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> Subject: Re: Paint booth
>>>
>>
>  Is this a K-12 school, or a community college. Adult education usually
>>> defaults to a B-occupancy, then goes to special occupancies or uses. If
>>> it
>>> is a high school it should be an E-occupancy.
>>>
>>
>  Spraying in an E-occupancy normally requires a paint spray room. Booths
>>> are not an option in E occupancies. See IFC 2404.2, IBC, IMC, and adopted
>>> electrical code.
>>>
>>
>  Was the booth installed under benefit of permit?
>>>
>>
>  bv
>>>
>>
>  ----- Original Message -----
>>> From: "Steve Leyton" <[email protected]>
>>> To: sprinklerforum@lists.**firespr**inkler.org<http://firesprinkler.org>
>>> <sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> Sent: Friday, July 26, 2013 12:14:37 PM
>>> Subject: RE: Paint booth
>>>
>>
>  Not sure there's a recognized 90 minute assembly. There are one and two
>>> hour, but I think the architect would have a hard time gaining approval
>>> for a 90 minute assembly without an appeal or approval of alternative
>>> means and methods of construction. For this type of booth (we've done 3
>>> in
>>> high schools recently) the industry standard for pre manufactured is
>>> either one or two hour.
>>>
>>
>  Steve
>>>
>>
>  "J.P. Merlino" <[email protected]> wrote:
>>>
>>
>  Can the room design method be applied provided the walls of the room in
>>> which the paint booth is located, are 90 min fire rated ?
>>>
>>
>  If the room is under 2500 sq ft it will make a big difference in the water
>>> supply and storage.
>>>
>>
>  J.P. Merlino
>>>
>>
>  -----Mensaje original----- De: sprinklerforum-bounces@lists.****
>>> firesprinkler.org 
>>> <sprinklerforum-bounces@lists.**firesprinkler.org<[email protected]>
>>> >
>>> [mailto:sprinklerforum-****[email protected].****org<
>>> sprinklerforum-bounces@**lists.firesprinkler.org<[email protected]>
>>> >]
>>> En nombre de Steve
>>> Leyton
>>> Enviado el: viernes, 26 de julio de 2013 02:10 p.m.
>>> Para: sprinklerforum@lists.**firespr**inkler.org<http://firesprinkler.org>
>>> <sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> ;
>>> sprinklerforum@lists.**firespr**inkler.org <http://firesprinkler.org><
>>> sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> Asunto: RE: Paint booth
>>>
>>
>  Yes, but if it's not rated I would say you need to do a design for EH II
>>> that encompasses the booth, the mixing room, and adjacent spaces
>>> (assuming
>>> no 2-hour separations from adjacent uses) up to the required design area
>>> in
>>> 11.2.3.1.1.
>>>
>>
>  Steve Leyton
>>> Protection Design & Consulting
>>> San Diego, CA
>>>
>>
>
>  -----Original Message----- From: sprinklerforum-bounces@lists.****
>>> firesprinkler.org 
>>> <sprinklerforum-bounces@lists.**firesprinkler.org<[email protected]>>
>>> on
>>> behalf of Douglas
>>> Hicks
>>> Sent: Fri 7/26/2013 10:09 AM
>>> To: sprinklerforum@lists.**firespr**inkler.org<http://firesprinkler.org>
>>> <sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> Subject: Paint booth
>>>
>>
>  I have been asked by a local school district about protecting an
>>> automotive
>>> paint booth. The catch, the booth is 2 x 4 framed, covered with sheet
>>> rock.
>>> The exhaust duct work does not have filters, and the exhaust fan may not
>>> be
>>> rated for hazardous paint fumes. The booth does not meet any UL
>>> standards,
>>> so I cannot install a dry chemical suppression system. Will a water
>>> based
>>> sprinkler work?
>>> ______________________________****_________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.**firespr**inkler.org <http://firesprinkler.org><
>>> Sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> http://lists.firesprinkler.****org/listinfo.cgi/**
>>> sprinklerforum-firesprinkler.**o<http://lists.firesprinkler.**
>>> org/listinfo.cgi/**sprinklerforum-firesprinkler.o<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o>
>>> **>
>>> rg
>>>
>>
>  ______________________________****_________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.**firespr**inkler.org <http://firesprinkler.org><
>>> Sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> http://lists.firesprinkler.****org/listinfo.cgi/**
>>> sprinklerforum-firesprinkler.**o<http://lists.firesprinkler.**
>>> org/listinfo.cgi/**sprinklerforum-firesprinkler.o<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o>
>>> **>
>>> rg
>>>
>>
>
>  ----- No se encontraron virus en este mensaje.
>>> Comprobado por AVG - www.avg.com
>>> Version: 2013.0.2904 / Base de datos de virus: 3209/6522 - Fecha de
>>> publicacion: 07/26/13
>>>
>>
>  ______________________________****_________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.**firespr**inkler.org <http://firesprinkler.org><
>>> Sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> http://lists.firesprinkler.****org/listinfo.cgi/**
>>> sprinklerforum-firesprinkler.**o<http://lists.firesprinkler.**
>>> org/listinfo.cgi/**sprinklerforum-firesprinkler.o<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o>
>>> **>
>>> rg
>>>
>>
>  ______________________________****_________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.**firespr**inkler.org <http://firesprinkler.org><
>>> Sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> http://lists.firesprinkler.****org/listinfo.cgi/**
>>> sprinklerforum-firesprinkler.****org<http://lists.**
>>> firesprinkler.org/listinfo.**cgi/sprinklerforum-**firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>>> >
>>> ______________________________****_________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.**firespr**inkler.org <http://firesprinkler.org><
>>> Sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> http://lists.firesprinkler.****org/listinfo.cgi/**
>>> sprinklerforum-firesprinkler.****org<http://lists.**
>>> firesprinkler.org/listinfo.**cgi/sprinklerforum-**firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>>> >
>>> ______________________________****_________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.**firespr**inkler.org <http://firesprinkler.org><
>>> Sprinklerforum@**lists.firesprinkler.org<[email protected]>
>>> >
>>> http://lists.firesprinkler.****org/listinfo.cgi/**
>>> sprinklerforum-firesprinkler.****org<http://lists.**
>>> firesprinkler.org/listinfo.**cgi/sprinklerforum-**firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>>> >
>>>
>>
>
>
>
>
>
>
> --
> Best regards,
> Charles                            mailto:[email protected]
>
>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.**firesprinkler.org<[email protected]>
> http://lists.firesprinkler.**org/listinfo.cgi/**
> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.**firesprinkler.org<[email protected]>
> http://lists.firesprinkler.**org/listinfo.cgi/**
> sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to