What would be simple and helpful would be a table similar to the one used
for sizing fire pump Suction/Discharge/Relief Valve Piping etc.

Since you are not measuring pressure, you could say 2" up to X gallons,
2.5" for Y etc....

A 2-1/2" Main drain is much easier and cheaper than some of the arrangments
left / required on backflow preventers.

Greg


On Mon, Jul 29, 2013 at 12:46 PM, Ron Greenman <[email protected]>wrote:

> Better but it is still interpretable as requiring a measured flow be
> established (if using the main drain location then the BOR design data).
> Then you'd need a port that flowed that much, main drain or otherwise, and
> then measure your annual test against anticipated flow to make sure you are
> meeting or exceeding the required flow. Or am I missing something? I'm
> pretty certain that newer fire service rated backflows don't fail any more
> often than normal FS checks, and that that type of failure is either
> catastrophic (doesn't open or barely opens) wouldn't a simple main drain
> test with decent flow demonstrate that the valve is working? just a Forum
> question as this is a done deal and I wasn't invited to join the exclusive
> 25 club.
>
>
> On Mon, Jul 29, 2013 at 7:11 AM, Roland Huggins
> <[email protected]>wrote:
>
> > the next edition has been cleaned-up on this issue.
> >
> > _______________________________________________________________ 25-271
> Log
> > #CP15 Final Action: Accept
> > (13.6.2.1, 13.6.2.2 (New))
> > _______________________________________________________________
> Submitter:
> > Technical Committee on Inspection, Testing, and Maintenance of
> Water-Based
> > Systems,
> >
> > Recommendation: Revise 13.6.2.1 to read as follows:
> > 13.6.2.1 All backflow preventers installed in fire protection system
> > piping shall be exercised annually by conducting a forward flow test at a
> > minimum flow rate of the system design.
> > Add new 13.6.2.2 and renumber subsequent sections accordingly:
> > 13.6.2.2 Where hydrants or inside hose stations are located downstream of
> > the backflow preventer, the forward flow test shall include hose stream
> > demand. Substantiation: This change was needed to better reflect that the
> > backflow preventer is not a precise test whereby the flow through it must
> > be measured but effort to exercise the device at flows as near as
> possible
> > to the system demand.
> > Committee Meeting Action: Accept
> > Number Eligible to Vote: 33
> > Ballot Results: Affirmative: 32 Negative: 1
> > Explanation of Negative:
> >
> > RAY, R.: This proposal should have been accepted in principle: the
> wording
> > “at a minimum flow rate” is confusing and should be reworded.
> > _______________________________________________________________ 25-272
> Log
> > #121 Final Action: Accept
> >
> > (13.6.2.1.1)
> >
> > _______________________________________________________________
> Submitter:
> > Roland J. Huggins, American Fire Sprinkler Association, Inc.
> > Recommendation: Delete the following text:
> >
> > 13.6.2.1.1 For backflow preventers sized 2 in. (50 mm) and under, the
> > forward flow test shall be acceptable to conduct without measuring flow,
> > where the test outlet is of a size to flow the system demand.
> > Substantiation: This section implies that a measured flow is required for
> > Backflow preventers (BFP) larger than 2 in when nothing in 13.6.2.1
> states
> > such a requirement. There are other means to identify that the system
> > demand is flowing through the BFP as discussed in A.13.6.2.1 It also
> needs
> > to be kept in mind that we are simply exercising the BFP to ensure it
> will
> > fully open at approximately the system demand. A high degree of accuracy
> > regarding the volume of water is not warranted. Additionally, BFP’s are
> > subjected to an annual internal inspection as part of the cross
> connection
> > protection program. Committee Meeting Action: Accept
> > Number Eligible to Vote: 33
> > Ballot Results: Affirmative: 33
> >
> >
> >
> > Roland Huggins, PE - VP Engineering
> >
> > American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> > Dallas, TX
> > http://www.firesprinkler.org
> >
> >
> >
> >
> >
> > On Jul 26, 2013, at 2:57 PM, Dwight Havens <[email protected]>
> wrote:
> >
> > > Then they ought to say that in the code language.
> > >
> > > Dwight
> > >
> > >
> > >
> > >
> > > ________________________________
> > > From: John Denhardt <[email protected]>
> > > To: "[email protected]" <
> > [email protected]>
> > > Sent: Thursday, July 25, 2013 3:07 PM
> > > Subject: RE: SIGN for Backflow Prevention Assembly Forward Flow Test
> > >
> > >
> > > While I do disagree to some extent of what the NFPA 25 committee has
> > done, Roland statement is correct.  I have had numerous discussions with
> > NFPA 25 committee members where they have stated the intent was to
> exercise
> > the device at near system demand.  The key word to me was "Exercise".
> > >
> > > John
> > >
> > > John August Denhardt, P.E., FSFPE
> > > Strickland Fire Protection Incorporated
> > > 5113 Berwyn Road
> > > College Park, Maryland 20740
> > > Office Telephone Number:  301-474-1136
> > > Mobile Telephone Number:  301-343-1457
> > > FIRE SPRINKLERS SAVE LIVES - Can you live without them?
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Forest
> Wilson
> > > Sent: Thursday, July 25, 2013 2:42 PM
> > > To: [email protected]
> > > Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
> > >
> > > Here is an email on this topic that Roland addressed in the past:
> > >
> > > Im not going to say it was one of those casual assumptions that all
> > > systems are calculated nor that all risers have placards.  The main
> > > thing to keep in mind that the intent is simply to fully EXERCISE the
> > > BFP at what os expected to be the system demand.  If no data
> > > available, a discussion with the AHJ is warranted.  As for benchmarks,
> > > only the flow is pertinent and pressure is irrelevant.
> > >
> > > Roland
> > >
> > > On Dec 22, 2009, at 2:44 PM, Matthew J. Willis wrote:
> > >
> > >>>
> > >>> On a more important matter: If a system was retrofitted with a
> > >>> backflow,
> > >> and
> > >>> there is no hydraulic calc plaque attached to the riser, and NFPA
> > >>> requires
> > >>> forward flow testing of backflows, how can you conduct the test
> > >>> without a
> > >>> benchmark to test against?
> > >>>
> > >>> What is the recommended practice in this scenario?
> > >>> Forest Wilson
> > >
> > > Sent from my iPhone
> > >
> > > On Jul 25, 2013, at 12:16 PM, Ron Greenman <[email protected]>
> > wrote:
> > >
> > >> Then subjective good flow demonstrates a working valve? If so all the
> > >> numbers bantered around are pretty meaningless.
> > >>
> > >>
> > >>
> > >> On Thu, Jul 25, 2013 at 8:07 AM, Forest Wilson <[email protected]
> > >wrote:
> > >>
> > >>> No.
> > >>> The intent is not to pitot the output but to exercise the valve.
> > >>>
> > >>>
> > >>> Sent from my iPhone
> > >>>
> > >>> On Jul 25, 2013, at 10:56 AM, Ron Greenman <[email protected]>
> > wrote:
> > >>>
> > >>>> Forest. What were you flowing to discover these failures? Main drain
> > or
> > >>>> some special test header? Would a sign with the data requested by
> the
> > >>>> customer that started this thread have had any utility in helping
> you
> > >>>> discover the problem?
> > >>>>
> > >>>> Then back to that perennial question of what's a "full flow " test
> and
> > >>> how
> > >>>> do you do one? I think Roland said the intent was to flow an
> > equivalent
> > >>> to
> > >>>> the design discharge criteria. How do you do this? Do we run a pitot
> > >>>> somewhere on the system? Do we catch and measure discharge? If so,
> > from
> > >>>> where? How do we arrange the test port(s)? Do we flow the design
> area
> > or
> > >>>> simulate it elsewhere? Do we need results of at least or better flow
> > or
> > >>>> right on the money flow? If not either of those how do we judge?
> > >>>>
> > >>>> Doesn't the hydraulic data plate note the required psi per the calcs
> > at
> > >>> the
> > >>>> BOR and the static? Isn't the difference the residual drop at that
> > point
> > >>>> relative to the design area? Wouldn't a main drain with good flow
> at a
> > >>> psi
> > >>>> around the BOR rating, and returning to close to the noted static
> when
> > >>>> terminated suggest a fully open valve, or an adequately open valve
> if
> > the
> > >>>> UG is oversized? In the latter case the partially open valve is
> > >>> equivalent
> > >>>> to fully open for the system I just described. Am I missing
> something
> > >>> here?
> > >>>> An erroneous a priori? My understanding of hydraulics wrong? Main
> > drains
> > >>>> are too small to simulate the result of all design area heads
> flowing
> > as
> > >>>> the water passes through the BOR?
> > >>>>
> > >>>>
> > >>>> On Thu, Jul 25, 2013 at 7:34 AM, Forest Wilson <
> [email protected]
> > >>>> wrote:
> > >>>>
> > >>>>> I still have the check valve from a Ames that failed to open.
> > >>>>> It was jammed shut, discovered when I was called out because they
> > >>> couldn't
> > >>>>> do the fire pump test.
> > >>>>>
> > >>>>> In another case, I tested a backflow and it failed (on a Best Buy
> > >>> store).
> > >>>>> I opened the valve up and the check was damaged, would only open a
> > >>> third.
> > >>>>>
> > >>>>>
> > >>>>>
> > >>>>> Sent from my iPhone
> > >>>>>
> > >>>>> On Jul 24, 2013, at 8:53 PM, Ron Greenman <[email protected]>
> > >>> wrote:
> > >>>>>
> > >>>>>> Worked well for plumbing and process piping applications as they
> are
> > >>>>>> constantly being exercised.
> > >>>>>>
> > >>>>>>
> > >>>>>> On Wed, Jul 24, 2013 at 5:12 PM, Dwight Havens <
> > [email protected]
> > >>>>>> wrote:
> > >>>>>>
> > >>>>>>> I do remember the ones with the rods in the center of the valve
> > being
> > >>>>>>> particularly poor.
> > >>>>>>>
> > >>>>>>> Dwight
> > >>>>>>>
> > >>>>>>>
> > >>>>>>>
> > >>>>>>>
> > >>>>>>> ________________________________
> > >>>>>>> From: Ron Greenman <[email protected]>
> > >>>>>>> To: [email protected]
> > >>>>>>> Sent: Tuesday, July 23, 2013 11:25 PM
> > >>>>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow
> > Test
> > >>>>>>>
> > >>>>>>>
> > >>>>>>> By the mid-nineties you have the early Ames models purpose built
> > for
> > >>>>>>> sprinklers readily available, but many units being installed are
> > still
> > >>>>> not
> > >>>>>>> listed for fire service as many jurisdictions don't consider the
> > fire
> > >>>>> line
> > >>>>>>> a fire line until after the backflow, and a n on-listed device is
> > >>>>> cheaper
> > >>>>>>> than a listed one. Plus many go back to the seventies and many
> used
> > >>>>> weights
> > >>>>>>> instead of springs and complicated lever systems for joining the
> > >>>>> clappers
> > >>>>>>> and weights. Wish I could post a picture.
> > >>>>>>>
> > >>>>>>>
> > >>>>>>> On Tue, Jul 23, 2013 at 7:33 PM, Dwight Havens <
> > [email protected]
> > >>>>>>>> wrote:
> > >>>>>>>
> > >>>>>>>> Give me a time frame. My best recollection is the mid '90's.
> > >>>>>>>>
> > >>>>>>>> Dwight
> > >>>>>>>>
> > >>>>>>>>
> > >>>>>>>>
> > >>>>>>>>
> > >>>>>>>> ________________________________
> > >>>>>>>> From: Ron Greenman <[email protected]>
> > >>>>>>>> To: [email protected]
> > >>>>>>>> Sent: Tuesday, July 23, 2013 9:12 PM
> > >>>>>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow
> > Test
> > >>>>>>>>
> > >>>>>>>>
> > >>>>>>>> Were these the plumbing type before fire service listed devices
> > >>>>> existed.
> > >>>>>>>>
> > >>>>>>>>
> > >>>>>>>> On Tue, Jul 23, 2013 at 4:32 PM, Dwight Havens <
> > >>> [email protected]
> > >>>>>>>>> wrote:
> > >>>>>>>>
> > >>>>>>>>> Yes, yes, and yes.  The original proposal was based on observed
> > >>>>>>> failures
> > >>>>>>>>> of BFPAs to operate properly during main drain testing.
> > >>>>>>>>>
> > >>>>>>>>> Glendale, AZ public library specifically comes to mind.
> > >>>>>>>>>
> > >>>>>>>>> Dwight
> > >>>>>>>>>
> > >>>>>>>>>
> > >>>>>>>>>
> > >>>>>>>>>
> > >>>>>>>>> ________________________________
> > >>>>>>>>> From: Todd Williams <[email protected]>
> > >>>>>>>>> To: "[email protected]" <
> > >>>>>>>>> [email protected]>
> > >>>>>>>>> Sent: Monday, July 22, 2013 9:32 PM
> > >>>>>>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow
> > Test
> > >>>>>>>>>
> > >>>>>>>>>
> > >>>>>>>>> Has there ever been an instance of system failure due to the
> > >>> backflow
> > >>>>>>> not
> > >>>>>>>>> properly opening? How about detection of a BFP problem during a
> > full
> > >>>>>>> flow
> > >>>>>>>>> test. How about something subsequent to the initial acceptance?
> > >>>>>>>>>
> > >>>>>>>>> Todd G Williams, PE
> > >>>>>>>>> Fire Protection Design/Consulting
> > >>>>>>>>> Stonington, CT
> > >>>>>>>>> 860-535-2080
> > >>>>>>>>> www.fpdc.com
> > >>>>>>>>>
> > >>>>>>>>> _______________________________________________
> > >>>>>>>>> Sprinklerforum mailing list
> > >>>>>>>>> [email protected]
> > >>>>>>>>>
> > >>>>>>>>>
> > >>>>>>>>
> > >>>>>>>
> > >>>>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>>>>>>> _______________________________________________
> > >>>>>>>>> Sprinklerforum mailing list
> > >>>>>>>>> [email protected]
> > >>>>>>>>>
> > >>>>>>>>>
> > >>>>>>>>
> > >>>>>>>
> > >>>>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>>>>>>>
> > >>>>>>>>
> > >>>>>>>>
> > >>>>>>>>
> > >>>>>>>> --
> > >>>>>>>> Ron Greenman
> > >>>>>>>> Instructor
> > >>>>>>>> Fire Protection Engineering Technology
> > >>>>>>>> Bates Technical College
> > >>>>>>>> 1101 So. Yakima Ave.
> > >>>>>>>> Tacoma, WA 98405
> > >>>>>>>>
> > >>>>>>>> [email protected]
> > >>>>>>>>
> > >>>>>>>> http://www.bates.ctc.edu/fireprotection/
> > >>>>>>>>
> > >>>>>>>> 253.680.7346
> > >>>>>>>> 253.576.9700 (cell)
> > >>>>>>>>
> > >>>>>>>> Member:
> > >>>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC,
> WFSC
> > >>>>>>>>
> > >>>>>>>> They are happy men whose natures sort with their vocations.
> > -Francis
> > >>>>>>> Bacon,
> > >>>>>>>> essayist, philosopher, and statesman (1561-1626)
> > >>>>>>>> _______________________________________________
> > >>>>>>>> Sprinklerforum mailing list
> > >>>>>>>> [email protected]
> > >>>>>>>>
> > >>>>>>>>
> > >>>>>>>
> > >>>>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>>>>>> _______________________________________________
> > >>>>>>>> Sprinklerforum mailing list
> > >>>>>>>> [email protected]
> > >>>>>>>>
> > >>>>>>>>
> > >>>>>>>
> > >>>>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>>>>>>
> > >>>>>>>
> > >>>>>>>
> > >>>>>>>
> > >>>>>>> --
> > >>>>>>> Ron Greenman
> > >>>>>>> Instructor
> > >>>>>>> Fire Protection Engineering Technology
> > >>>>>>> Bates Technical College
> > >>>>>>> 1101 So. Yakima Ave.
> > >>>>>>> Tacoma, WA 98405
> > >>>>>>>
> > >>>>>>> [email protected]
> > >>>>>>>
> > >>>>>>> http://www.bates.ctc.edu/fireprotection/
> > >>>>>>>
> > >>>>>>> 253.680.7346
> > >>>>>>> 253.576.9700 (cell)
> > >>>>>>>
> > >>>>>>> Member:
> > >>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> > >>>>>>>
> > >>>>>>> They are happy men whose natures sort with their vocations.
> > -Francis
> > >>>>> Bacon,
> > >>>>>>> essayist, philosopher, and statesman (1561-1626)
> > >>>>>>> _______________________________________________
> > >>>>>>> Sprinklerforum mailing list
> > >>>>>>> [email protected]
> > >>>>>>>
> > >>>>>>>
> > >>>>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>>>>> _______________________________________________
> > >>>>>>> Sprinklerforum mailing list
> > >>>>>>> [email protected]
> > >>>>>>>
> > >>>>>>>
> > >>>>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>>>>>
> > >>>>>>
> > >>>>>>
> > >>>>>>
> > >>>>>> --
> > >>>>>> Ron Greenman
> > >>>>>> Instructor
> > >>>>>> Fire Protection Engineering Technology
> > >>>>>> Bates Technical College
> > >>>>>> 1101 So. Yakima Ave.
> > >>>>>> Tacoma, WA 98405
> > >>>>>>
> > >>>>>> [email protected]
> > >>>>>>
> > >>>>>> http://www.bates.ctc.edu/fireprotection/
> > >>>>>>
> > >>>>>> 253.680.7346
> > >>>>>> 253.576.9700 (cell)
> > >>>>>>
> > >>>>>> Member:
> > >>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> > >>>>>>
> > >>>>>> They are happy men whose natures sort with their vocations.
> -Francis
> > >>>>> Bacon,
> > >>>>>> essayist, philosopher, and statesman (1561-1626)
> > >>>>>> _______________________________________________
> > >>>>>> Sprinklerforum mailing list
> > >>>>>> [email protected]
> > >>>>>>
> > >>>>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>>> _______________________________________________
> > >>>>> Sprinklerforum mailing list
> > >>>>> [email protected]
> > >>>>>
> > >>>>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>>>
> > >>>>
> > >>>>
> > >>>>
> > >>>> --
> > >>>> Ron Greenman
> > >>>> Instructor
> > >>>> Fire Protection Engineering Technology
> > >>>> Bates Technical College
> > >>>> 1101 So. Yakima Ave.
> > >>>> Tacoma, WA 98405
> > >>>>
> > >>>> [email protected]
> > >>>>
> > >>>> http://www.bates.ctc.edu/fireprotection/
> > >>>>
> > >>>> 253.680.7346
> > >>>> 253.576.9700 (cell)
> > >>>>
> > >>>> Member:
> > >>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> > >>>>
> > >>>> They are happy men whose natures sort with their vocations. -Francis
> > >>> Bacon,
> > >>>> essayist, philosopher, and statesman (1561-1626)
> > >>>> _______________________________________________
> > >>>> Sprinklerforum mailing list
> > >>>> [email protected]
> > >>>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>> _______________________________________________
> > >>> Sprinklerforum mailing list
> > >>> [email protected]
> > >>>
> > >>>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >>>
> > >>
> > >>
> > >>
> > >> --
> > >> Ron Greenman
> > >> Instructor
> > >> Fire Protection Engineering Technology
> > >> Bates Technical College
> > >> 1101 So. Yakima Ave.
> > >> Tacoma, WA 98405
> > >>
> > >> [email protected]
> > >>
> > >> http://www.bates.ctc.edu/fireprotection/
> > >>
> > >> 253.680.7346
> > >> 253.576.9700 (cell)
> > >>
> > >> Member:
> > >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> > >>
> > >> They are happy men whose natures sort with their vocations. -Francis
> > Bacon,
> > >> essayist, philosopher, and statesman (1561-1626)
> > >> _______________________________________________
> > >> Sprinklerforum mailing list
> > >> [email protected]
> > >>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>