That isn't what the intent of the code is as stated.....just flow at system
demand. I can only speak for us, but we do a LOT of risers with only a 250
gpm or so demand...sometimes even less.

A 4" drain is well over what we need to open it up enough for system
demand. I would bet a 2" drain gets really close.


On Mon, Jul 29, 2013 at 2:52 PM, David Autry <[email protected]> wrote:

> Wouldn't it be easier, if you have a 4" backflow preventer you run 4" out
> the wall, 3" BFP, 3" out the wall, etc...
> That should open her up all the way.
>
>
> David Autry
>
> Meininger Fire Protection Inc.
> 2521 W L St. Suite No.4
> Lincoln, Ne 68522
> Voice (402) 466-2616
> Fax (402) 466-2617
> [email protected]
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg
> McGahan
> Sent: Monday, July 29, 2013 2:35 PM
> To: [email protected]
> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>
> What would be simple and helpful would be a table similar to the one used
> for sizing fire pump Suction/Discharge/Relief Valve Piping etc.
>
> Since you are not measuring pressure, you could say 2" up to X gallons,
> 2.5" for Y etc....
>
> A 2-1/2" Main drain is much easier and cheaper than some of the
> arrangments left / required on backflow preventers.
>
> Greg
>
>
> On Mon, Jul 29, 2013 at 12:46 PM, Ron Greenman
> <[email protected]>wrote:
>
> > Better but it is still interpretable as requiring a measured flow be
> > established (if using the main drain location then the BOR design data).
> > Then you'd need a port that flowed that much, main drain or otherwise,
> > and then measure your annual test against anticipated flow to make
> > sure you are meeting or exceeding the required flow. Or am I missing
> > something? I'm pretty certain that newer fire service rated backflows
> > don't fail any more often than normal FS checks, and that that type of
> > failure is either catastrophic (doesn't open or barely opens) wouldn't
> > a simple main drain test with decent flow demonstrate that the valve
> > is working? just a Forum question as this is a done deal and I wasn't
> > invited to join the exclusive
> > 25 club.
> >
> >
> > On Mon, Jul 29, 2013 at 7:11 AM, Roland Huggins
> > <[email protected]>wrote:
> >
> > > the next edition has been cleaned-up on this issue.
> > >
> > > _______________________________________________________________
> > > 25-271
> > Log
> > > #CP15 Final Action: Accept
> > > (13.6.2.1, 13.6.2.2 (New))
> > > _______________________________________________________________
> > Submitter:
> > > Technical Committee on Inspection, Testing, and Maintenance of
> > Water-Based
> > > Systems,
> > >
> > > Recommendation: Revise 13.6.2.1 to read as follows:
> > > 13.6.2.1 All backflow preventers installed in fire protection system
> > > piping shall be exercised annually by conducting a forward flow test
> > > at a minimum flow rate of the system design.
> > > Add new 13.6.2.2 and renumber subsequent sections accordingly:
> > > 13.6.2.2 Where hydrants or inside hose stations are located
> > > downstream of the backflow preventer, the forward flow test shall
> > > include hose stream demand. Substantiation: This change was needed
> > > to better reflect that the backflow preventer is not a precise test
> > > whereby the flow through it must be measured but effort to exercise
> > > the device at flows as near as
> > possible
> > > to the system demand.
> > > Committee Meeting Action: Accept
> > > Number Eligible to Vote: 33
> > > Ballot Results: Affirmative: 32 Negative: 1 Explanation of Negative:
> > >
> > > RAY, R.: This proposal should have been accepted in principle: the
> > wording
> > > "at a minimum flow rate" is confusing and should be reworded.
> > > _______________________________________________________________
> > > 25-272
> > Log
> > > #121 Final Action: Accept
> > >
> > > (13.6.2.1.1)
> > >
> > > _______________________________________________________________
> > Submitter:
> > > Roland J. Huggins, American Fire Sprinkler Association, Inc.
> > > Recommendation: Delete the following text:
> > >
> > > 13.6.2.1.1 For backflow preventers sized 2 in. (50 mm) and under,
> > > the forward flow test shall be acceptable to conduct without
> > > measuring flow, where the test outlet is of a size to flow the system
> demand.
> > > Substantiation: This section implies that a measured flow is
> > > required for Backflow preventers (BFP) larger than 2 in when nothing
> > > in 13.6.2.1
> > states
> > > such a requirement. There are other means to identify that the
> > > system demand is flowing through the BFP as discussed in A.13.6.2.1
> > > It also
> > needs
> > > to be kept in mind that we are simply exercising the BFP to ensure
> > > it
> > will
> > > fully open at approximately the system demand. A high degree of
> > > accuracy regarding the volume of water is not warranted.
> > > Additionally, BFP's are subjected to an annual internal inspection
> > > as part of the cross
> > connection
> > > protection program. Committee Meeting Action: Accept Number Eligible
> > > to Vote: 33 Ballot Results: Affirmative: 33
> > >
> > >
> > >
> > > Roland Huggins, PE - VP Engineering
> > >
> > > American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves
> Lives
> > > Dallas, TX
> > > http://www.firesprinkler.org
> > >
> > >
> > >
> > >
> > >
> > > On Jul 26, 2013, at 2:57 PM, Dwight Havens <[email protected]>
> > wrote:
> > >
> > > > Then they ought to say that in the code language.
> > > >
> > > > Dwight
> > > >
> > > >
> > > >
> > > >
> > > > ________________________________
> > > > From: John Denhardt <[email protected]>
> > > > To: "[email protected]" <
> > > [email protected]>
> > > > Sent: Thursday, July 25, 2013 3:07 PM
> > > > Subject: RE: SIGN for Backflow Prevention Assembly Forward Flow
> > > > Test
> > > >
> > > >
> > > > While I do disagree to some extent of what the NFPA 25 committee
> > > > has
> > > done, Roland statement is correct.  I have had numerous discussions
> > > with NFPA 25 committee members where they have stated the intent was
> > > to
> > exercise
> > > the device at near system demand.  The key word to me was "Exercise".
> > > >
> > > > John
> > > >
> > > > John August Denhardt, P.E., FSFPE
> > > > Strickland Fire Protection Incorporated
> > > > 5113 Berwyn Road
> > > > College Park, Maryland 20740
> > > > Office Telephone Number:  301-474-1136 Mobile Telephone Number:
> > > > 301-343-1457 FIRE SPRINKLERS SAVE LIVES - Can you live without
> > > > them?
> > > >
> > > > -----Original Message-----
> > > > From: [email protected] [mailto:
> > > [email protected]] On Behalf Of Forest
> > Wilson
> > > > Sent: Thursday, July 25, 2013 2:42 PM
> > > > To: [email protected]
> > > > Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow
> > > > Test
> > > >
> > > > Here is an email on this topic that Roland addressed in the past:
> > > >
> > > > Im not going to say it was one of those casual assumptions that
> > > > all systems are calculated nor that all risers have placards.  The
> > > > main thing to keep in mind that the intent is simply to fully
> > > > EXERCISE the BFP at what os expected to be the system demand.  If
> > > > no data available, a discussion with the AHJ is warranted.  As for
> > > > benchmarks, only the flow is pertinent and pressure is irrelevant.
> > > >
> > > > Roland
> > > >
> > > > On Dec 22, 2009, at 2:44 PM, Matthew J. Willis wrote:
> > > >
> > > >>>
> > > >>> On a more important matter: If a system was retrofitted with a
> > > >>> backflow,
> > > >> and
> > > >>> there is no hydraulic calc plaque attached to the riser, and
> > > >>> NFPA requires forward flow testing of backflows, how can you
> > > >>> conduct the test without a benchmark to test against?
> > > >>>
> > > >>> What is the recommended practice in this scenario?
> > > >>> Forest Wilson
> > > >
> > > > Sent from my iPhone
> > > >
> > > > On Jul 25, 2013, at 12:16 PM, Ron Greenman <[email protected]>
> > > wrote:
> > > >
> > > >> Then subjective good flow demonstrates a working valve? If so all
> > > >> the numbers bantered around are pretty meaningless.
> > > >>
> > > >>
> > > >>
> > > >> On Thu, Jul 25, 2013 at 8:07 AM, Forest Wilson
> > > >> <[email protected]
> > > >wrote:
> > > >>
> > > >>> No.
> > > >>> The intent is not to pitot the output but to exercise the valve.
> > > >>>
> > > >>>
> > > >>> Sent from my iPhone
> > > >>>
> > > >>> On Jul 25, 2013, at 10:56 AM, Ron Greenman
> > > >>> <[email protected]>
> > > wrote:
> > > >>>
> > > >>>> Forest. What were you flowing to discover these failures? Main
> > > >>>> drain
> > > or
> > > >>>> some special test header? Would a sign with the data requested
> > > >>>> by
> > the
> > > >>>> customer that started this thread have had any utility in
> > > >>>> helping
> > you
> > > >>>> discover the problem?
> > > >>>>
> > > >>>> Then back to that perennial question of what's a "full flow "
> > > >>>> test
> > and
> > > >>> how
> > > >>>> do you do one? I think Roland said the intent was to flow an
> > > equivalent
> > > >>> to
> > > >>>> the design discharge criteria. How do you do this? Do we run a
> > > >>>> pitot somewhere on the system? Do we catch and measure
> > > >>>> discharge? If so,
> > > from
> > > >>>> where? How do we arrange the test port(s)? Do we flow the
> > > >>>> design
> > area
> > > or
> > > >>>> simulate it elsewhere? Do we need results of at least or better
> > > >>>> flow
> > > or
> > > >>>> right on the money flow? If not either of those how do we judge?
> > > >>>>
> > > >>>> Doesn't the hydraulic data plate note the required psi per the
> > > >>>> calcs
> > > at
> > > >>> the
> > > >>>> BOR and the static? Isn't the difference the residual drop at
> > > >>>> that
> > > point
> > > >>>> relative to the design area? Wouldn't a main drain with good
> > > >>>> flow
> > at a
> > > >>> psi
> > > >>>> around the BOR rating, and returning to close to the noted
> > > >>>> static
> > when
> > > >>>> terminated suggest a fully open valve, or an adequately open
> > > >>>> valve
> > if
> > > the
> > > >>>> UG is oversized? In the latter case the partially open valve is
> > > >>> equivalent
> > > >>>> to fully open for the system I just described. Am I missing
> > something
> > > >>> here?
> > > >>>> An erroneous a priori? My understanding of hydraulics wrong?
> > > >>>> Main
> > > drains
> > > >>>> are too small to simulate the result of all design area heads
> > flowing
> > > as
> > > >>>> the water passes through the BOR?
> > > >>>>
> > > >>>>
> > > >>>> On Thu, Jul 25, 2013 at 7:34 AM, Forest Wilson <
> > [email protected]
> > > >>>> wrote:
> > > >>>>
> > > >>>>> I still have the check valve from a Ames that failed to open.
> > > >>>>> It was jammed shut, discovered when I was called out because
> > > >>>>> they
> > > >>> couldn't
> > > >>>>> do the fire pump test.
> > > >>>>>
> > > >>>>> In another case, I tested a backflow and it failed (on a Best
> > > >>>>> Buy
> > > >>> store).
> > > >>>>> I opened the valve up and the check was damaged, would only
> > > >>>>> open a
> > > >>> third.
> > > >>>>>
> > > >>>>>
> > > >>>>>
> > > >>>>> Sent from my iPhone
> > > >>>>>
> > > >>>>> On Jul 24, 2013, at 8:53 PM, Ron Greenman
> > > >>>>> <[email protected]>
> > > >>> wrote:
> > > >>>>>
> > > >>>>>> Worked well for plumbing and process piping applications as
> > > >>>>>> they
> > are
> > > >>>>>> constantly being exercised.
> > > >>>>>>
> > > >>>>>>
> > > >>>>>> On Wed, Jul 24, 2013 at 5:12 PM, Dwight Havens <
> > > [email protected]
> > > >>>>>> wrote:
> > > >>>>>>
> > > >>>>>>> I do remember the ones with the rods in the center of the
> > > >>>>>>> valve
> > > being
> > > >>>>>>> particularly poor.
> > > >>>>>>>
> > > >>>>>>> Dwight
> > > >>>>>>>
> > > >>>>>>>
> > > >>>>>>>
> > > >>>>>>>
> > > >>>>>>> ________________________________
> > > >>>>>>> From: Ron Greenman <[email protected]>
> > > >>>>>>> To: [email protected]
> > > >>>>>>> Sent: Tuesday, July 23, 2013 11:25 PM
> > > >>>>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward
> > > >>>>>>> Flow
> > > Test
> > > >>>>>>>
> > > >>>>>>>
> > > >>>>>>> By the mid-nineties you have the early Ames models purpose
> > > >>>>>>> built
> > > for
> > > >>>>>>> sprinklers readily available, but many units being installed
> > > >>>>>>> are
> > > still
> > > >>>>> not
> > > >>>>>>> listed for fire service as many jurisdictions don't consider
> > > >>>>>>> the
> > > fire
> > > >>>>> line
> > > >>>>>>> a fire line until after the backflow, and a n on-listed
> > > >>>>>>> device is
> > > >>>>> cheaper
> > > >>>>>>> than a listed one. Plus many go back to the seventies and
> > > >>>>>>> many
> > used
> > > >>>>> weights
> > > >>>>>>> instead of springs and complicated lever systems for joining
> > > >>>>>>> the
> > > >>>>> clappers
> > > >>>>>>> and weights. Wish I could post a picture.
> > > >>>>>>>
> > > >>>>>>>
> > > >>>>>>> On Tue, Jul 23, 2013 at 7:33 PM, Dwight Havens <
> > > [email protected]
> > > >>>>>>>> wrote:
> > > >>>>>>>
> > > >>>>>>>> Give me a time frame. My best recollection is the mid '90's.
> > > >>>>>>>>
> > > >>>>>>>> Dwight
> > > >>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>> ________________________________
> > > >>>>>>>> From: Ron Greenman <[email protected]>
> > > >>>>>>>> To: [email protected]
> > > >>>>>>>> Sent: Tuesday, July 23, 2013 9:12 PM
> > > >>>>>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward
> > > >>>>>>>> Flow
> > > Test
> > > >>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>> Were these the plumbing type before fire service listed
> > > >>>>>>>> devices
> > > >>>>> existed.
> > > >>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>> On Tue, Jul 23, 2013 at 4:32 PM, Dwight Havens <
> > > >>> [email protected]
> > > >>>>>>>>> wrote:
> > > >>>>>>>>
> > > >>>>>>>>> Yes, yes, and yes.  The original proposal was based on
> > > >>>>>>>>> observed
> > > >>>>>>> failures
> > > >>>>>>>>> of BFPAs to operate properly during main drain testing.
> > > >>>>>>>>>
> > > >>>>>>>>> Glendale, AZ public library specifically comes to mind.
> > > >>>>>>>>>
> > > >>>>>>>>> Dwight
> > > >>>>>>>>>
> > > >>>>>>>>>
> > > >>>>>>>>>
> > > >>>>>>>>>
> > > >>>>>>>>> ________________________________
> > > >>>>>>>>> From: Todd Williams <[email protected]>
> > > >>>>>>>>> To: "[email protected]" <
> > > >>>>>>>>> [email protected]>
> > > >>>>>>>>> Sent: Monday, July 22, 2013 9:32 PM
> > > >>>>>>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward
> > > >>>>>>>>> Flow
> > > Test
> > > >>>>>>>>>
> > > >>>>>>>>>
> > > >>>>>>>>> Has there ever been an instance of system failure due to
> > > >>>>>>>>> the
> > > >>> backflow
> > > >>>>>>> not
> > > >>>>>>>>> properly opening? How about detection of a BFP problem
> > > >>>>>>>>> during a
> > > full
> > > >>>>>>> flow
> > > >>>>>>>>> test. How about something subsequent to the initial
> acceptance?
> > > >>>>>>>>>
> > > >>>>>>>>> Todd G Williams, PE
> > > >>>>>>>>> Fire Protection Design/Consulting Stonington, CT
> > > >>>>>>>>> 860-535-2080
> > > >>>>>>>>> www.fpdc.com
> > > >>>>>>>>>
> > > >>>>>>>>> _______________________________________________
> > > >>>>>>>>> Sprinklerforum mailing list
> > > >>>>>>>>> [email protected]
> > > >>>>>>>>>
> > > >>>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>
> > > >>>>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>>>>>>>> _______________________________________________
> > > >>>>>>>>> Sprinklerforum mailing list
> > > >>>>>>>>> [email protected]
> > > >>>>>>>>>
> > > >>>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>
> > > >>>>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>> --
> > > >>>>>>>> Ron Greenman
> > > >>>>>>>> Instructor
> > > >>>>>>>> Fire Protection Engineering Technology Bates Technical
> > > >>>>>>>> College
> > > >>>>>>>> 1101 So. Yakima Ave.
> > > >>>>>>>> Tacoma, WA 98405
> > > >>>>>>>>
> > > >>>>>>>> [email protected]
> > > >>>>>>>>
> > > >>>>>>>> http://www.bates.ctc.edu/fireprotection/
> > > >>>>>>>>
> > > >>>>>>>> 253.680.7346
> > > >>>>>>>> 253.576.9700 (cell)
> > > >>>>>>>>
> > > >>>>>>>> Member:
> > > >>>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM,
> > > >>>>>>>> WFC,
> > WFSC
> > > >>>>>>>>
> > > >>>>>>>> They are happy men whose natures sort with their vocations.
> > > -Francis
> > > >>>>>>> Bacon,
> > > >>>>>>>> essayist, philosopher, and statesman (1561-1626)
> > > >>>>>>>> _______________________________________________
> > > >>>>>>>> Sprinklerforum mailing list
> > > >>>>>>>> [email protected]
> > > >>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>
> > > >>>>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>>>>>>> _______________________________________________
> > > >>>>>>>> Sprinklerforum mailing list
> > > >>>>>>>> [email protected]
> > > >>>>>>>>
> > > >>>>>>>>
> > > >>>>>>>
> > > >>>>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>>>>>>>
> > > >>>>>>>
> > > >>>>>>>
> > > >>>>>>>
> > > >>>>>>> --
> > > >>>>>>> Ron Greenman
> > > >>>>>>> Instructor
> > > >>>>>>> Fire Protection Engineering Technology Bates Technical
> > > >>>>>>> College
> > > >>>>>>> 1101 So. Yakima Ave.
> > > >>>>>>> Tacoma, WA 98405
> > > >>>>>>>
> > > >>>>>>> [email protected]
> > > >>>>>>>
> > > >>>>>>> http://www.bates.ctc.edu/fireprotection/
> > > >>>>>>>
> > > >>>>>>> 253.680.7346
> > > >>>>>>> 253.576.9700 (cell)
> > > >>>>>>>
> > > >>>>>>> Member:
> > > >>>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC,
> > > >>>>>>> WFSC
> > > >>>>>>>
> > > >>>>>>> They are happy men whose natures sort with their vocations.
> > > -Francis
> > > >>>>> Bacon,
> > > >>>>>>> essayist, philosopher, and statesman (1561-1626)
> > > >>>>>>> _______________________________________________
> > > >>>>>>> Sprinklerforum mailing list
> > > >>>>>>> [email protected]
> > > >>>>>>>
> > > >>>>>>>
> > > >>>>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>>>>>> _______________________________________________
> > > >>>>>>> Sprinklerforum mailing list
> > > >>>>>>> [email protected]
> > > >>>>>>>
> > > >>>>>>>
> > > >>>>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>>>>>>
> > > >>>>>>
> > > >>>>>>
> > > >>>>>>
> > > >>>>>> --
> > > >>>>>> Ron Greenman
> > > >>>>>> Instructor
> > > >>>>>> Fire Protection Engineering Technology Bates Technical
> > > >>>>>> College
> > > >>>>>> 1101 So. Yakima Ave.
> > > >>>>>> Tacoma, WA 98405
> > > >>>>>>
> > > >>>>>> [email protected]
> > > >>>>>>
> > > >>>>>> http://www.bates.ctc.edu/fireprotection/
> > > >>>>>>
> > > >>>>>> 253.680.7346
> > > >>>>>> 253.576.9700 (cell)
> > > >>>>>>
> > > >>>>>> Member:
> > > >>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC,
> > > >>>>>> WFSC
> > > >>>>>>
> > > >>>>>> They are happy men whose natures sort with their vocations.
> > -Francis
> > > >>>>> Bacon,
> > > >>>>>> essayist, philosopher, and statesman (1561-1626)
> > > >>>>>> _______________________________________________
> > > >>>>>> Sprinklerforum mailing list
> > > >>>>>> [email protected]
> > > >>>>>>
> > > >>>>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>>>> _______________________________________________
> > > >>>>> Sprinklerforum mailing list
> > > >>>>> [email protected]
> > > >>>>>
> > > >>>>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>>>>
> > > >>>>
> > > >>>>
> > > >>>>
> > > >>>> --
> > > >>>> Ron Greenman
> > > >>>> Instructor
> > > >>>> Fire Protection Engineering Technology Bates Technical College
> > > >>>> 1101 So. Yakima Ave.
> > > >>>> Tacoma, WA 98405
> > > >>>>
> > > >>>> [email protected]
> > > >>>>
> > > >>>> http://www.bates.ctc.edu/fireprotection/
> > > >>>>
> > > >>>> 253.680.7346
> > > >>>> 253.576.9700 (cell)
> > > >>>>
> > > >>>> Member:
> > > >>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC,
> > > >>>> WFSC
> > > >>>>
> > > >>>> They are happy men whose natures sort with their vocations.
> > > >>>> -Francis
> > > >>> Bacon,
> > > >>>> essayist, philosopher, and statesman (1561-1626)
> > > >>>> _______________________________________________
> > > >>>> Sprinklerforum mailing list
> > > >>>> [email protected]
> > > >>>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>> _______________________________________________
> > > >>> Sprinklerforum mailing list
> > > >>> [email protected]
> > > >>>
> > > >>>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > >>>
> > > >>
> > > >>
> > > >>
> > > >> --
> > > >> Ron Greenman
> > > >> Instructor
> > > >> Fire Protection Engineering Technology Bates Technical College
> > > >> 1101 So. Yakima Ave.
> > > >> Tacoma, WA 98405
> > > >>
> > > >> [email protected]
> > > >>
> > > >> http://www.bates.ctc.edu/fireprotection/
> > > >>
> > > >> 253.680.7346
> > > >> 253.576.9700 (cell)
> > > >>
> > > >> Member:
> > > >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> > > >>
> > > >> They are happy men whose natures sort with their vocations.
> > > >> -Francis
> > > Bacon,
> > > >> essayist, philosopher, and statesman (1561-1626)
> > > >> _______________________________________________
> > > >> Sprinklerforum mailing list
> > > >> [email protected]
> > > >>
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > >
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > >
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > >
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> > >
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> > Bacon, essayist, philosopher, and statesman (1561-1626)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
> rg
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to