Are you saying "Stupid is as stupid does"?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On Jul 30, 2013, at 7:03 PM, Roland Huggins <[email protected]> wrote:

> It's hard to compete against Forrest Gump but that is what the standard says. 
>  The TC often assumes every knows what they mean and that no one would do 
> something stupid.
> 
> Roland
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
> 
> 
> 
> 
> 
> On Jul 30, 2013, at 3:10 PM, Todd - Work <[email protected]> wrote:
> 
>> Then you have to deal with someone who cites Section 22.4.4.7 (9) which 
>> states that the fitting that is attached to the sprinkler head shall be 
>> excluded from the hydraulics. Would you not include a 1/2" extension in the 
>> calcs? There was one yahoo out in this area who tried to use that section to 
>> exclude Flexheads from the calcs since a Flexhead is a fitting. 
>> 
>> Todd G Williams, PE
> 