Ran into this once before...I don't think there is anything "wrong" with the arrangement because you can always close the two system control valves to service, but I believe backflow assemblies are listed as assemblies and if the discharge side control valve is not installed it seems as though it would void the listing.
Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Thursday, August 01, 2013 9:23 AM To: [email protected] Subject: Valves on BFP I'm on the road and don't have all my code stuff so I would appreciate a little help. I am looking at an existing riser with the following sequence of material: OS&Y, backflow preventer, Tee to FDC, then to 2 risers, each with control valve and alarm valve. There is no valve on the discharge of the BFP other than the aforementioned butterfly valves. Is that acceptable? It doesn't seems right but don't have any specific reference. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org