With no control vale on the discharge of the backflow, my guess is that this voids the BFP listing.
John John August Denhardt, P.E., FSFPE Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Number: 301-343-1457 FIRE SPRINKLERS SAVE LIVES - Can you live without them? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Thursday, August 01, 2013 10:23 AM To: [email protected] Subject: Valves on BFP I'm on the road and don't have all my code stuff so I would appreciate a little help. I am looking at an existing riser with the following sequence of material: OS&Y, backflow preventer, Tee to FDC, then to 2 risers, each with control valve and alarm valve. There is no valve on the discharge of the BFP other than the aforementioned butterfly valves. Is that acceptable? It doesn't seems right but don't have any specific reference. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org