These don say exactly what the ahj is looking for. We changed 20 SR heads
in one compartment with new QR heads because they were painted or damaged
and now he wants calcs because we did not replace them with exactly the
same thing.

He finally said that if we could show him they were identical except for
response time he would allow them.



On Fri, Aug 2, 2013 at 1:52 PM, Ron Greenman <[email protected]> wrote:

> http://www.vikinggroupinc.com/techarticles/thermal.pdf
>
>
> http://www.ahcancal.org/facility_operations/fire_life_safety/Pages/QuickResponseSHvsStandardSH.aspx
>
>
> On Fri, Aug 2, 2013 at 11:43 AM, Greg McGahan <[email protected]>
> wrote:
>
> > Does anyone have documetnation in an easy to read format that shows the
> > difference in SR SSP/U and QR SSP/U heads is ONLY the response time and
> > that all other aspects are identical - spray pattern, spacing
> requirements,
> > deflector distance etc?
> >
> > Thanks,
> > Greg
> >
> > --
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to