Being a Californian and having sprinklered countless wood-framed
buildings, I can tell you that we have done these "split" complements"
many, many times.  Sprinklers in a pocket above the rated envelope, no
sprinklers in the plenum, sprinklers in the ceiling below.  

You want to hear really melodic cursing in Spanish?  Watch a finishing
crew that has to meticulously mud sheetrock up to the firestop
assemblies at each of the dozens of drops that penetrate that one-hour
lid at the top of the plenum space.   


Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Monday, August 05, 2013 11:53 AM
To: [email protected]
Subject: Re: Special Situations (8.15)

So if the joisting is wood, but encapsulated by 5/8 type X GWB then the
assembly is still considered combustible? What if enough layers (three I
think) to get a 2-hr rating?


On Mon, Aug 5, 2013 at 11:32 AM, Roland Huggins
<[email protected]>wrote:

> Granted as pointed out that everything else must also be non- or 
> limited-combustible but it's a moot point since it is WOOD JOIST 
> construction.  Focusing on the outer membrane doesn't change the fact 
> that the assembly is combustible construction.
>
> Roland
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves
Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On Aug 5, 2013, at 7:26 AM, Brian Harris <[email protected]>
> wrote:
>
> > All-
> > I recently finished a design for a wood structure day care facility,

> > (1)
> level of attic heads and (1) level of ceiling heads. The GC has now 
> decided in an effort to save money on the HVAC to attach drywall to 
> the bottom of the wood joist and use the area between this drywall and

> the suspended ceiling as a return air plenum. If I'm reading 8.1.1.2.1

> & 8.15.1.2.2 correctly I do not need to add a 3rd level of protection
in this "plenum"
> area correct?
> >
> > Brian Harris, CET
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to