Subject: Special Situations (8.15)

All-
I recently finished a design for a wood structure day care facility, (1) level 
of attic heads and (1) level of ceiling heads. The GC has now decided in an 
effort to save money on the HVAC to attach drywall to the bottom of the wood 
joist and use the area between this drywall and the suspended ceiling as a 
return air plenum. If I'm reading 8.1.1.2.1 & 8.15.1.2.2 correctly I do not 
need to add a 3rd level of protection in this "plenum" area correct?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to