Granted as pointed out that everything else must also be non- or 
limited-combustible but it's a moot point since it is WOOD JOIST construction.  
Focusing on the outer membrane doesn't change the fact that the assembly is 
combustible construction.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 5, 2013, at 7:26 AM, Brian Harris <[email protected]> wrote:

> All-
> I recently finished a design for a wood structure day care facility, (1) 
> level of attic heads and (1) level of ceiling heads. The GC has now decided 
> in an effort to save money on the HVAC to attach drywall to the bottom of the 
> wood joist and use the area between this drywall and the suspended ceiling as 
> a return air plenum. If I'm reading 8.1.1.2.1 & 8.15.1.2.2 correctly I do not 
> need to add a 3rd level of protection in this "plenum" area correct?
> 
> Brian Harris, CET