And a city with high rises usually, at least around here, will have a whole
lot of amendments to IBC & NFPA. So look for those also.


On Tue, Aug 13, 2013 at 8:54 AM, Johnson, Duane (NIH/OD/ORS) [C] <
[email protected]> wrote:

> For those that don't have it.
>
> 3.3.3.1.1 Fire Department Connection for Automatic Standpipe Systems.   A
> connection through which the fire department can pump the secondary water
> supply to an automatic standpipe system at the required system demand.
> Supplemental water can also be provided into the sprinkler system or other
> system furnishing water for fire extinguishment to supplement existing
> water supplies.
>
> 7.7.2   Where an automatic or semiautomatic water supply is required for a
> Class I, II, or III standpipe system by Section 5.4, the standpipe system
> shall be designed so that the system demand can be independently supplied
> by the attached water supply and each fire department connection provided
> on the system.
>
> And to complete the loop:
> 5.4.1.2    Class I standpipe systems in buildings classified as high-rise
> buildings shall be automatic or semiautomatic.
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor)
> Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: Johnson, Duane (NIH/OD/ORS) [C]
> Sent: Tuesday, August 13, 2013 11:35 AM
> To: '[email protected]'
> Subject: RE: High rise- non seismic zone - 2 water supplies?
>
> Yes, but don't overlook NFPA 14...particularly 3.3.3.1.1 (13 ed) and 7.7.2.
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor) Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: [email protected] [mailto:[email protected]]
> Sent: Tuesday, August 13, 2013 11:24 AM
> To: [email protected]
> Subject: RE: High rise- non seismic zone - 2 water supplies?
>
> An FDC "can pump supplemental water" 3.8.1.4 (2013). By definition a
> supplement is added to something. Not a replacement or a second water
> supply?
>
> Sorry I couldn't resist the opportunity to take a dig at the FDC
> definition in 13.
>
> Ron F
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Martinez,
> Dewayne
> Sent: Tuesday, August 13, 2013 8:10 AM
> To: [email protected]
> Subject: RE: High rise- non seismic zone - 2 water supplies?
>
> Thanks, I never know about section 104.10
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Johnson, Duane (NIH/OD/ORS) [C]
> Sent: Tuesday, August 13, 2013 9:11 AM
> To: [email protected]
> Subject: RE: High rise- non seismic zone - 2 water supplies?
>
> Then the IBC requires a connection to two water mains or two connections
> to one water main so that interruption to service can be isolated so that
> the water supply will not be interrupted.
>
> Section 104.10 can be used by the owner. This gives the building official
> a provision to grant a modification do due practical difficulties. By
> lessening compliance with the section above, the modification will not
> lessen fire protection or life safety, it only lessens reliability. After
> all, there is an FDC...
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor) Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: Martinez, Dewayne [mailto:[email protected]]
> Sent: Tuesday, August 13, 2013 10:02 AM
> To: [email protected]
> Subject: RE: High rise- non seismic zone - 2 water supplies?
>
> Complete remodel of the building forcing them to bring it up to current
> code.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Johnson, Duane (NIH/OD/ORS) [C]
> Sent: Tuesday, August 13, 2013 7:56 AM
> To: [email protected]
> Subject: RE: High rise- non seismic zone - 2 water supplies?
>
> What has caused the need to go back and sprinkler??
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor) Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: Johnson, Duane (NIH/OD/ORS) [C]
> Sent: Tuesday, August 13, 2013 8:55 AM
> To: [email protected]
> Subject: RE: High rise- non seismic zone - 2 water supplies?
>
> Section 403.3.2 requires a high rise with a fire pump to be connected to a
> minimum of two water mains. There is a performance based exception however.
>
> Section 903.3.5.2 requires an additional "on-site" water supply for new
> high rise buildings in seismic zones C, D, E or F. The "on-site" water
> supply is different from the water supply that is brought "to the site"
> (ie underground water main). There is an exception for existing buildings.
> The requirement is to increase reliability in the event of a seismic
> activity.
>
> Over to you Steve...
>
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor) Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: Martinez, Dewayne [mailto:[email protected]]
> Sent: Monday, August 12, 2013 5:57 PM
> To: [email protected]
> Subject: High rise- non seismic zone - 2 water supplies?
>
> IBC (09ed) sections 403 and 903
>
> I have an existing un-sprinkled high rise building that now needs to be
> fully sprinkled per NFPA 13 (07ed) and will require a fire pump.  I think
> it will require two sources of water supply but I just want to confirm.
>
> Section 403.3 requires a secondary water supply where required by
> 903.3.5.2.
>
> 903.3.5.2 requires 2 sources if I am in a seismic zone, which I am not,
> but 403.3.2 seems to trump this by requiring a second supply when a fire
> pump is installed.  Am I interpreting this correctly?
>
> Thanks,
>
> Dewayne
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)