To extend Steve's comments, it is necessary to document that valve exists 
between two lead ins, and why. In an ideal world, this would extend to the 
water purveyors design and maintenance software. Section valves are reliable, 
particularly if exercised on schedule, but this valve is outside the owner's 
control, or even awareness. A water department could easily decide to not 
repair an "unnecessary" valve that is stuck in the open position. 

bv 

----- Original Message -----
From: "Steve Leyton" <[email protected]> 
To: [email protected] 
Sent: Tuesday, August 13, 2013 11:06:52 AM 
Subject: RE: High rise- non seismic zone - 2 water supplies? 

I don't disagree with it arbitrarily, just don't approve it 
unconditionally. I think it depends on how the main in question is 
supplied by the water system zone source; can each side of the proposed 
sectional valve location independently supply the demand? If it's 
symmetrically yes, then I don't oppose that approach. 


Steve Leyton 




-----Original Message----- 
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
Martinez, Dewayne 
Sent: Tuesday, August 13, 2013 11:00 AM 
To: [email protected] 
Subject: RE: High rise- non seismic zone - 2 water supplies? 

I was going to propose the same idea to the AHJ. With the water main in 
front of the building being supplied from different mains at either end 
I thought of putting a sectional valve between the two water lead in's 
to be able to isolate each service. Sounds like you don't agree with 
that, how come? 

-----Original Message----- 
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
Steve Leyton 
Sent: Tuesday, August 13, 2013 12:14 PM 
To: [email protected] 
Subject: RE: High rise- non seismic zone - 2 water supplies? 

The intent of two laterals being in case of interruption of the 
municipal water supply. But we've already seen some interesting 
interps; one project here in San Diego was only bounded by one city 
main, so they dug up the street, put a sectional valve in the public 
main between to lateral connections, as justified it as being capable of 
supply from two different legs of the muni system. 


Steve Leyton 




-----Original Message----- 
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
Johnson, Duane (NIH/OD/ORS) [C] 
Sent: Tuesday, August 13, 2013 7:11 AM 
To: [email protected] 
Subject: RE: High rise- non seismic zone - 2 water supplies? 

Then the IBC requires a connection to two water mains or two connections 
to one water main so that interruption to service can be isolated so 
that the water supply will not be interrupted. 

Section 104.10 can be used by the owner. This gives the building 
official a provision to grant a modification do due practical 
difficulties. By lessening compliance with the section above, the 
modification will not lessen fire protection or life safety, it only 
lessens reliability. After all, there is an FDC... 

Duane Johnson, PE 
Program Manager 
Division of the Fire Marshal (Contractor) Office of Research Services 
National Institutes of Health 
301-496-0487 

"Protecting Science - One Sprinkler at a Time" 


-----Original Message----- 
From: Martinez, Dewayne [mailto:[email protected]] 
Sent: Tuesday, August 13, 2013 10:02 AM 
To: [email protected] 
Subject: RE: High rise- non seismic zone - 2 water supplies? 

Complete remodel of the building forcing them to bring it up to current 
code. 

-----Original Message----- 
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
Johnson, Duane (NIH/OD/ORS) [C] 
Sent: Tuesday, August 13, 2013 7:56 AM 
To: [email protected] 
Subject: RE: High rise- non seismic zone - 2 water supplies? 

What has caused the need to go back and sprinkler?? 

Duane Johnson, PE 
Program Manager 
Division of the Fire Marshal (Contractor) Office of Research Services 
National Institutes of Health 
301-496-0487 

"Protecting Science - One Sprinkler at a Time" 


-----Original Message----- 
From: Johnson, Duane (NIH/OD/ORS) [C] 
Sent: Tuesday, August 13, 2013 8:55 AM 
To: [email protected] 
Subject: RE: High rise- non seismic zone - 2 water supplies? 

Section 403.3.2 requires a high rise with a fire pump to be connected to 
a minimum of two water mains. There is a performance based exception 
however. 

Section 903.3.5.2 requires an additional "on-site" water supply for new 
high rise buildings in seismic zones C, D, E or F. The "on-site" water 
supply is different from the water supply that is brought "to the site" 
(ie underground water main). There is an exception for existing 
buildings. The requirement is to increase reliability in the event of a 
seismic activity. 

Over to you Steve... 


Duane Johnson, PE 
Program Manager 
Division of the Fire Marshal (Contractor) Office of Research Services 
National Institutes of Health 
301-496-0487 

"Protecting Science - One Sprinkler at a Time" 


-----Original Message----- 
From: Martinez, Dewayne [mailto:[email protected]] 
Sent: Monday, August 12, 2013 5:57 PM 
To: [email protected] 
Subject: High rise- non seismic zone - 2 water supplies? 

IBC (09ed) sections 403 and 903 

I have an existing un-sprinkled high rise building that now needs to be 
fully sprinkled per NFPA 13 (07ed) and will require a fire pump. I 
think it will require two sources of water supply but I just want to 
confirm. 

Section 403.3 requires a secondary water supply where required by 
903.3.5.2. 

903.3.5.2 requires 2 sources if I am in a seismic zone, which I am not, 
but 403.3.2 seems to trump this by requiring a second supply when a fire 
pump is installed. Am I interpreting this correctly? 

Thanks, 

Dewayne 



_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler 
.org 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler 
.org 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler 
.org 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler 
.org 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler 
.org 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler 
.org 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler 
.org 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to