Since carousels are not addressed in 13 it is more interesting and challenging. 

Greg

Sent from my iPhone

On Sep 4, 2013, at 8:12 AM, Todd - Work <[email protected]> wrote:

> Greg,
> 
> I haven't run into this situation before, but I've done a few tire stores. A 
> possibility would be to design the sprinklers for the tire storage on each 
> level and put a water curtain around the opening. Also an interlock to shut 
> down the carousel. You might have to increase the density over the opening as 
> well as you noted. Challenging situation. Look at requirements for protecting 
> conveyors to see if that gives you insight. 
> 
> Disclaimer: This is a guess based on limited knowledge. Take it as such.
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 
> On Sep 4, 2013, at 8:29 AM, Greg McGahan <[email protected]> wrote:
> 
>> No takers? Anybody home?
>> 
>> 
>> On Tue, Sep 3, 2013 at 6:06 PM, Greg McGahan <[email protected]> wrote:
>> 
>>> Scenario - a 2 story building
>>> 
>>> There is a vertical tire carousel that goes through a mezzanine – hole
>>> sized at 6’-4 x approx. 17’ which sits in the corner of the storage area
>>> (general car parts) – to the 2nd floor. – The entire height of the
>>> carousel is 18-7” from the ground level.
>>> 
>>> If we were to place a row of sprinklers along the wall (nothing above
>>> them  all the way to the 2nd floor ceiling) and then on the opposite side
>>> under the mezzanine, could we in effect comply with NFPA #13 2007 ed -
>>> Table 18.4(a) (6) - for one row of in rack sprinklers so we could calculate
>>> the system on the 2nd floor at .40 gpm?
>>> 
>>> This is a strange deal to me because it would seem like overkill to have a
>>> .90 density to protect such a small area and then increase it by 15’-0 on
>>> the 2 sides as required.
>>> 
>>> Thanks for your help
>>> 
>>> 
>>> --
>>> Greg McGahan
>>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>>> 1160 McKenzie Road
>>> Cantonment, FL 32533
>>> 850-937-1850
>>> fax 850-937-1852
>> 
>> 
>> 
>> -- 
>> Greg McGahan
>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>> 1160 McKenzie Road
>> Cantonment, FL 32533
>> 850-937-1850
>> fax 850-937-1852
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to