They are using an existing 1/2" outlet (likely an upright) to supply a 
relocated sprinkler (likely a pendent)...completely legitimate. 

8.15.20.4.1 (2013)    When pipe schedule systems are revamped, a nipple not 
exceeding 4 in. (100 mm) in length shall be permitted to be installed in the 
branch line fitting.
8.15.20.4.2    All piping other than the nipple permitted in 8.15.20.4.1 and 
8.15.20.4.3 shall be a minimum of 1 in. (25 mm) in diameter in accordance with 
Figure 8.15.20.4.2.
8.15.20.4.3    When it is necessary to pipe two new ceiling sprinklers from an 
existing outlet in an overhead system, the use of a nipple not exceeding 4 in. 
(100 mm) in length and of the same pipe thread size as the existing outlet 
shall be permitted, provided that a hydraulic calculation verifies that the 
design flow rate will be achieved in accordance with Figure 8.15.20.4.3.
8.15.20.4.4    Where an armover is attached to connect to a sprinkler, the use 
of pipe nipples less than 1 in. (25 mm) in diameter shall not be permitted 
where seismic design is required on the system.

By the way, where did the sch 80 requirement come from? I have never been able 
to locate that in code.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Bobby Gillett [mailto:[email protected]] 
Sent: Thursday, September 05, 2013 10:46 PM
To: [email protected]
Subject: Re: Shoulder Nipple

Hoping they are requesting sch 80 and they are not in a seismic zone. 

Sent from my iPhone

On Sep 5, 2013, at 9:12 PM, "JSM Fire Pro" <[email protected]> wrote:

> You’re a third party glancing over a bill of materials for an 
> add/relocate day job.  You notice one of the line items is calling for 
> several ½”
> shoulder nipples. 
> 
> 
> 
> What goes through your mind?
> 
> 
> 
> J. Scott Mitchell, PE
> 
> B&W Technical Services Pantex
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to