Hello All,

For some reason we still have about half a box of 1/2" x Close Sch 80 nipples 
in the warehouse I ordered a while back. I remember seeing that somewhere but 
can't find it in NFPA 13 2010 or 2013. I know I would not have spent the extra 
money for them if I did not have to...

Friday, September 6, 2013, 9:41:27 AM, you wrote:

> As an "Old Time Fitter" from the early 70's to the 90's before I got 
> into design, I was taught to use Sch 80 nipples for the additional 
> strength that they had over the standard Sch 40.

> On 9/6/2013 5:53 AM, Bobby Gillett wrote:
>> Duane,

>> As I mentioned, I was going off of memory. Not sure where exactly the Sch.

>> 80 came from, maybe it was an old requirement for seismic areas before the

>> limitation of 1" diameter nipples was enforced?? May have been a company
>> requirement before that as where I was before was in a "seismic zone"...not
>> quite sure. Anybody else out there ever hear of that?



>> Bobby Gillett
>> *Living Water Fire Protection, LLC*
>> 1160 McKenzie Rd.
>> Cantonment, FL 32533
>> (850) 937-1850
>> livingwaterfp.com  <http://livingwaterfp.com/>


>> On Fri, Sep 6, 2013 at 5:31 AM, Johnson, Duane (NIH/OD/ORS) [C] <
>> [email protected]> wrote:

>>> They are using an existing 1/2" outlet (likely an upright) to supply a
>>> relocated sprinkler (likely a pendent)...completely legitimate.

>>> 8.15.20.4.1 (2013)    When pipe schedule systems are revamped, a nipple
>>> not exceeding 4 in. (100 mm) in length shall be permitted to be installed
>>> in the branch line fitting.
>>> 8.15.20.4.2    All piping other than the nipple permitted in 8.15.20.4.1
>>> and 8.15.20.4.3 shall be a minimum of 1 in. (25 mm) in diameter in
>>> accordance with Figure 8.15.20.4.2.
>>> 8.15.20.4.3    When it is necessary to pipe two new ceiling sprinklers
>>> from an existing outlet in an overhead system, the use of a nipple not
>>> exceeding 4 in. (100 mm) in length and of the same pipe thread size as the
>>> existing outlet shall be permitted, provided that a hydraulic calculation
>>> verifies that the design flow rate will be achieved in accordance with
>>> Figure 8.15.20.4.3.
>>> 8.15.20.4.4    Where an armover is attached to connect to a sprinkler, the
>>> use of pipe nipples less than 1 in. (25 mm) in diameter shall not be
>>> permitted where seismic design is required on the system.

>>> By the way, where did the sch 80 requirement come from? I have never been
>>> able to locate that in code.

>>> Duane Johnson, PE
>>> Program Manager
>>> Division of the Fire Marshal (Contractor)
>>> Office of Research Services
>>> National Institutes of Health
>>> 301-496-0487

>>> "Protecting Science - One Sprinkler at a Time"


>>> -----Original Message-----
>>> From: Bobby Gillett [mailto:[email protected]]
>>> Sent: Thursday, September 05, 2013 10:46 PM
>>> To: [email protected]
>>> Subject: Re: Shoulder Nipple

>>> Hoping they are requesting sch 80 and they are not in a seismic zone.

>>> Sent from my iPhone

>>> On Sep 5, 2013, at 9:12 PM, "JSM Fire Pro" <[email protected]> wrote:

>>>> You’re a third party glancing over a bill of materials for an
>>>> add/relocate day job.  You notice one of the line items is calling for
>>> several ½”
>>>> shoulder nipples.



>>>> What goes through your mind?



>>>> J. Scott Mitchell, PE

>>>> B&W Technical Services Pantex

>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>> er.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]

>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]

>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


>> -----
>> No virus found in this message.
>> Checked by AVG - www.avg.com
>> Version: 2013.0.3392 / Virus Database: 3222/6641 - Release Date: 09/05/13




> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-- 
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to