No. The building code requires, "All valves controlling the water supply ... " for automatic sprinkler systems, pumps, tanks, etc. be supervised. A test valve is not a fire protection water supply control valve.
Steve Leyton -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Wednesday, September 25, 2013 10:34 AM To: [email protected] Subject: Full Forward Flow Test Control Valves Without going back through the rest of the mile long thread....... IF there is a control valve in the normally closed position for Full Forward Flow Testing, is it REQUIRED to be monitored? Thanks, -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org