Here's what I found (NFPA 13 2013):
6.1.1.5 - isn't required to be listed, only approved.
6.7.1.3 - not required to be a listed indicating valve.
6.7.1.2 - not required to be 'slow-close'.
6.7.3 - must be 'approved'

So, being mostly design only, I don't have direct access to net pricing.
But if the above is correct, and if a 4" non-listed, non-slow-close valve
cost less than the typical listed 4" butterfly valve, I can't see why a
contractor can't consider using something similar to Nibco GD-4765
(http://www.nibco.com/Valves/Butterfly-Valves/Ductile-Iron-Butterfly-Valves/
GD-4765-Butterfly-Valve-Ductile-Iron-Grooved-300-PSI/).  Anybody see it
differently?  Any contractors want to price out the two different types of
valves and post the info?

Ed Kramer
Lawrence, KS

**
Next questions:  does it have to be 'listed' or just 'approved'?  Does it
have to be 'slow-close'?

Ed Kramer
Lawrence, KS

**
No. 

The building code requires, "All valves controlling the water supply ...
" for automatic sprinkler systems, pumps, tanks, etc. be supervised.   A
test valve is not a fire protection water supply control valve.  

Steve Leyton

**

Without going back through the rest of the mile long thread.......

IF there is a control valve in the normally closed position for Full Forward
Flow Testing,  is it REQUIRED to be monitored?

Thanks,

--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852