But the design is not compartment driven so how does that imply two compartments? Actually, it's to stop the rearward discharge from wetting the other sprinkler.
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Oct 3, 2013, at 6:33 AM, [email protected] wrote: > 13 (2013) 8.7.3.1.4 seems to support the lintel as a beam. > > 8.7.3.1.4 Sidewall spray sprinklers shall not be installed back-to-back > without being separated by a continuous lintel or soffit. > > Ron F _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org