But the design is not compartment driven so how does that imply two 
compartments?  Actually, it's to stop the rearward discharge from wetting the 
other sprinkler.

Roland
 
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Oct 3, 2013, at 6:33 AM, [email protected] wrote:

> 13 (2013) 8.7.3.1.4 seems to support the lintel as a beam.
> 
> 8.7.3.1.4    Sidewall spray sprinklers shall not be installed back-to-back 
> without being separated by a continuous lintel or soffit.
> 
> Ron F