First answer - no, protection of piping against damage from earthquakes is 
universal. 

As K.I.S.S. resources, I'm not sure it's that difficult, once you understand 
the process and the ASCE 7 standard it's pretty straightforward.  There is 
utility software out there to calculated the force factor that you need to 
start with and for calculating the brace assemblies.  Contact Tolco or Afcon 
(those are two that I know of, there may be more from other manufacturers) 
regarding their calc programs; go to USGS to download a force factor program.

Personally, I think the best "EQB For Dummies" primer you can find is probably 
Annex E of NFPA 13, 2013 edition.


Steve Leyton



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of JD Gamble
Sent: Tuesday, December 10, 2013 1:59 PM
To: [email protected]
Subject: [Blacklisted Sender] EQ Bracing

What are the best “Keep It Simple Stupid” resources for seismic applications?

And, ... is EQ bracing limited to only those floors above grade?



JD Gamble
Life Safety Solutions of Sheridan