John,

No need to hide.

I often get involved post design, someone else did the design, I'm QC or 3rd 
party reviewer and I start asking questions about questionable practices or 
designs where it's obvious that the right questions were never asked.  Then 
when I start pressing the issue I hear those very words, "The plans have 
already been approved by the Code official".  So of course that is supposed to 
make it OK to ignore basic code and design requirements, the exercise of due 
diligence and the practice of simple common sense.  The majority of the times 
it's not an actual error on the part of the code official.  If you review a 
plan for a simple building with an ordinary hazard I system you wouldn't think 
much about it.  But I'm looking at the rest of the project and see that the 
building houses 20 ft high racks with a combustible material handling process 
and dust collection equipment. NOT OH I by any stretch of the imagination.   
The other conversation I love, Owner:"but we didn't put sprinklers in our last 
building like this", Me:"when was that built?", owner:"1960".  

Anyway, don't want to take this thread down a rabbit trail just thought 
Roland's comment was kind of humorous but sadly true.


And now, back to our regularly scheduled 
discussion........................................

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John 
Drucker - Home
Sent: Monday, January 20, 2014 3:46 PM
To: [email protected]
Subject: RE: 1/2" and Seismic

Craig wrote; "I was not surprised at the first e-mail, that's what I hear all 
the time...  "the plan reviewer approved the plans", (even though they had 
significant technical errors)."

Craig, here's a question for ya, just finished my sixth cup......if the plan 
reviewer approved the plans that had significant technical errors what does 
that say about the technician who designed and the professional engineer who 
signed em ?

.....running for cover.

John


John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Red Bank, New Jersey



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, January 20, 2014 2:45 PM
To: [email protected]
Subject: RE: 1/2" and Seismic

I was not surprised at the first e-mail, that's what I hear all the time...
"the plan reviewer approved the plans", (even though they had significant 
technical errors).


Had me goin' for a minute.  

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland 
Huggins
Sent: Monday, January 20, 2014 2:39 PM
To: [email protected]
Subject: Re: 1/2" and Seismic

CORRECTION

that should read - an approved set of plans does NOT mean it's ok to violate
NFPA 13.   I've gotta lay off the coffee.

Thanks John for the rapid catch and polite direct contact.

Roland
  
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jan 20, 2014, at 11:33 AM, Roland Huggins <[email protected]>
wrote:

> DOn't forget that an approved set of plans means it is ok to violate 
> NFPA
13.  All an approved set of plans means is that you have permission to proceed. 
So, even when approved, if you install it, you are responsible for
it being right.    Now if there is an existing approved variance, all is
golden.
> 
> Roland
> 
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
> 
> 
> 
> 
> 
> On Jan 17, 2014, at 3:52 PM, Charles Thurston <[email protected]> wrote:
> 
>> This is an existing system. 1 1/2" branch with 1/2" outlet "T"s for
heads, They added a L/O ceiling 6" below the top of the pipe in the parking 
deck. Now need to nipple over to a Dry Wax Over Lead (Local Ordnance) Dry Head. 
Another contractor submitted plans, calcs and got a permit for this a 1/2" 
Close, 1/2" x 1" 90, 1' Close nipple, 1" T with plug for the head. The other 
contractor's foreman smarted off to one of the owners and they got thrown off 
the site. Material is all there, Just need the labor to put it in.
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________