I have been told that an attic in a school had so much wood that it should have 
been designed to OH2. This is by the "expert" investigating the fire that 
started at the roof and burned the building to the ground. Fortunately I was 
not the EOR. The EOR specified light hazard for the entire school (based on 
NFPA classification) but now claims that I am the expert and should have known 
better. So classifying occupancies is not simple as some take it to be. 
Tony 

----- Original Message -----
From: "Duane Johnson (NIH/OD/ORS) [C]" <[email protected]>
To: [email protected]
Sent: Monday, March 10, 2014 7:33:25 AM
Subject: RE: occupancy classification vs occupancy hazard

I don't know what is worse, a sprinkler technician assigning classification of 
occupancies playing the EOR role, an architect assigning classification of 
occupancies playing the EOR role, or an underqualified EOR assigning 
classification of occupancies playing the EOR role. 

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Monday, March 10, 2014 8:44 AM
To: [email protected]
Subject: RE: occupancy classification vs occupancy hazard

Understanding the hazards present is probably one of our biggest challenges.   
One of the biggest errors I deal with is incorrectly classified occupancies.    
People will look at the examples and NFPA 13 and really not expend a whole lot 
of time really asking pertinent questions regarding the use of areas.  Case in 
point was a fabrication plant, HUGE machine shop producing HUGE machine parts 
(parts that were in the 20-60 ton range).  60 ft tall building with 
warehousing.  The architects start their code analysis first, ask some 
questions and then assign the Building Code occupancy category.  Fire 
protection then determines requirements based on their analysis.  Unfortunately 
in this scenario FP got called in way late in the game.   Architects asked what 
was being stored in the warehouse, owner states steel tubing.  OK, no problem, 
non-combustible stuff, it's an S-2.  Owner's happy, NO SPRINKLERS!  

Only problem was there was almost 60 tons of combustible crating and foam 
packing around these "steel tubes".  So out the window with an S-2.  Now FP has 
to break the news that this WILL be a sprinklered building. 

You've got to ask questions, very specific questions.  Sadly I've found few 
designers and engineers who are capable or willing to play detective to the 
extent of being able to provide a substantiated occupancy classification for 
unusual occupancies.  Don't assume anything, ask questions, lots of questions.  
The list of hazards in NFPA is only the tip of the iceberg.  In the industrial 
world, the list is probably 25 years or more out of date.  Every day a new 
industry emerges that isn't anywhere on any list.  You have to do your research 
and your homework.   The last thing you want to see is your design project on 
the six-o-clock news.




Craig Prahl   



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad 
Casterline
Sent: Friday, March 07, 2014 7:57 PM
To: [email protected]
Subject: Re: occupancy classification vs occupancy hazard

BTW, there are (4) reasons why I posted this:
1) it is in the Body of 13
2) it comes with a Shall Not
3) it feels like it has 'over-all importance'
4) i am NICET certified, so I should thoroughly understand what I am 
responsible for applying

> On Mar 7, 2014, at 6:24 PM, Brad Casterline <[email protected]> wrote:
> 
> 
> 
>> On Mar 7, 2014, at 6:08 PM, Brad Casterline <[email protected]> wrote:
>> 
>> NFPA 13, 5.1.2 (i'm looking at 2007):
>> "Occupancy classifications shall not be intended to be a general 
>> classification of occupancy hazards".
>> 
>> I have finally said "well, uh, ok" to 5.1.1, but am still saying "huh?" to 
>> 5.1.2.
>> 
>> This is not a pressing issue, I am not trying to cause a stir, and I wish I 
>> had a real world hands on type something to share.
>> 
>> Happy Friday,
>> Brad
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to