I am close to letting it go, but only because I have a spreadsheet (that only I 
could love ;) ) you have it too Roland- the one I sent you about a week after 
you said Let's take this off forum-- you know- the whole new can of curiosity 
you opened for me with your " a more meaningful reference for activation time 
is in regard to the same RHR point on the different fire curves" ? 
It was the key to defining Combustibility for myself, and the reason I am a 
totally scatter-brained, very very sick man today- thanks for that ;).
Craig, having any luck on finding that hobby for me?

> On Mar 11, 2014, at 9:38 AM, Roland Huggins <[email protected]> 
> wrote:
> 
> We all love to define things in a quantified and fixed manner but if only it 
> where as simple as balancing the volume water discharged and the quantity of 
> fuel available.  This is accurate in a very broad and general sense but the 
> devil is in the details.  The PhD’s at NIST have been beating on this issue 
> for decades and we still don’t have the answer.
> 
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
> 
> 
> 
> 
> 
>> On Mar 11, 2014, at 6:11 AM, Brad Casterline <[email protected]> wrote:
>> 
>> I am hoping we can talk about something else soon. It is very well known how 
>> much heat it takes to vaporize how much water- when I wonder why .1 
>> gpm/s.f., knowing the heat of combustion for the type of combustibles in LH 
>> & OH is 13,100 kJ/kg of O2 consumed, I get ~5 lbs/s.f. Hospitals are 
>> ~6lb/s.f., meaning, I presume, there is a dab of OHI in ther
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to