I am looking at a building that has 12' ceilings (per floor). In one area there is a vertical opening to the second floor that is protected with closely spaced sprinklers and draft stops. Is it still acceptable to use the quick response area reduction or does the opening to the second floor count as a ceiling in excess of 20'?
If it is acceptable to use the quick response reduction, can you apply the reduction to the length of closely spaced sprinkler heads that must be calc'd? Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org