I would say yes and no.  It all depends on your selection of a design basis.  
The area below the opening has a tall ceiling so that PORTION of the building 
has a design basis that is not reduced.  The remainder of the building can use 
its own design basis that includes the reduction or follow the other.  
Naturally we are assuming the entire building is a single occupancy hazard 
classification.

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Apr 1, 2014, at 8:33 AM, Matt Grise <[email protected]> wrote:

> I am looking at a building that has 12' ceilings (per floor). In one area 
> there is a vertical opening to the second floor that is protected with 
> closely spaced sprinklers and draft stops. Is it still acceptable to use the 
> quick response area reduction or does the opening to the second floor count 
> as a ceiling in excess of 20'?
> 
> If it is acceptable to use the quick response reduction, can you apply the 
> reduction to the length of closely spaced sprinkler heads that must be calc'd?
> 
> Matt Grisé PE*, LEED AP, NICET II  
> Sales Engineer 
> Alliance Fire Protection 
> 130 w 9th Ave.
> North Kansas City, MO 64116
> 
> *Licensed in KS & MO 
> 
> 913.888.0647 ph 
> 913.888.0618 f 
> 913.927.0222 cell 
> www. AFPsprink.com 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to