*3.7.1* Obstructed Construction. *Panel construction and other

construction where beams, trusses, or other members impede

heat flow or water distribution in a manner that materially affects
the ability of sprinklers to control or suppress a fire.

*A.3.7.1 Obstructed Construction. *The following are examples

of obstructed construction. The definitions are provided to assist

the user in determining the type of construction feature.

(1) *Beam and Girder Construction*. The term *beam and girder construction*

as used in this standard includes noncombustible

and combustible roof or floor decks supported by wood

beams of 4 in. (102 mm) or greater nominal thickness or

concrete or steel beams spaced 3 ft to 71⁄2 ft (0.9mto 2.3 m)

on center and either supported on or framed into girders.

[Where supporting a wood plank deck, this includes semimill

and panel construction, and where supporting (with

steel framing) gypsum plank, steel deck, concrete, tile, or

similar material, this includes much of the so-called noncombustible

construction.]



*8.8.4.1.2 Obstructed Construction. *Under obstructed construction,

the sprinkler deflector shall be located in accordance

with one of the following arrangements:

(3) Installed in each bay of obstructed construction, with the

deflectors located a minimum of 1 in. (25.4 mm) and a

maximum of 12 in. (305 mm) below the ceiling.


R/

Matt





On Tue, Jul 15, 2014 at 10:24 AM, Fairchild, Jack <
[email protected]> wrote:

> What's the true time duration of this sim?
>
> Jack Fairchild
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brad
> Casterline
> Sent: Tuesday, July 15, 2014 10:13 AM
> To: [email protected]
> Subject: RE: ECOH 20x20 OH1 Obstructed Construction
>
> Max would be 22" (16" deep beam + 6"). Minimum would be 13" because If I
> looked at 13 right at 3'9 from the beam the deflector can be max 3" above
> the bottom.
> .2m cell is how 'fine' the calculation domain is, .1*3.28=4", so I can
> only 'resolve' to an accuracy of 4" increments. I first set this up using
> .05m cells so I could look at activation time for 286F Standard Response at
> 22", but that calc was taking several days to complete and I lost patience.
> Just because we CAN be 22" down in this situation, doesn't mean we should
> :).
> I think it is always best to be as high as possible without the flow being
> obstructed because not only is the activation faster, the pattern hits
> higher up, like on a couch against a wall!
> Brad
>
> -----Original Message-----
> From: Matthew Willis [mailto:[email protected]]
> Sent: Tuesday, July 15, 2014 8:57 AM
> To: [email protected]
> Subject: Re: ECOH 20x20 OH1 Obstructed Construction
>
> *Published on Jul 15, 2014*
>
> 20x20x10 room. ECOH sprinkler centered. 16" steel I beams 3'-9" from
> center. Max deflector is 22", and Min is 3" above bottom of beams= 13" ,
> but deflector distance is closer to 12" due to .2m cell size. OH1 figured
> here, 400 x.15=60 GPM, K=11.2.
> Activation time difference between min and max deflector distance is not
> part of this movie- instead, the sim is to show suppression time for the
> flow rate if the head activated when the heat release rate is 2750 kW.
> Wall Temperature and Water Drop Temperature are displayed.
> I used E_COEFFICIENT=2.
>
>
> Correction-- .1m cells, so deflector distance can be 12", 16", 20", or 24".
> Walls and ceiling are gyp. bd., floor is carpet. Doors are 3x7.
> K=11.2?
>
>
>
> I might be looking incorrectly, but in your heading you state obstructed
> construction. This allows 17" - 22" from deck. Your second comments state
> between cells and you list 12, 16, 20, and 24. Doesn't cell spacing not
> limit us to 1-12"
>
>
> R/
>
> Matt
>
>
>
>
> On Tue, Jul 15, 2014 at 9:11 AM, Brad Casterline <[email protected]>
> wrote:
>
> > https://www.youtube.com/watch?v=B-Gj7V3hCyM&feature=youtu.be
> >
> >
> >
> > Movie anyone?
> >
> >
> >
> > Brad Casterline, NICET IV
> >
> > Fire Protection Division
> >
> >
> >
> > FSC, Inc.
> >
> > P: 913-722-3473
> >
> > [email protected]
> >
> > www.fsc-inc.com
> >
> >
> >
> > Engineering Solutions for the Built Environment
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to