Hmm Matt, I used (1), but then raised it to 3" above the bottom of beam in
accordance with Table 8.8.5.1.2. (2007) 
Is that a mistake?

Brad

-----Original Message-----
From: Matthew Willis [mailto:[email protected]] 
Sent: Tuesday, July 15, 2014 9:33 AM
To: [email protected]
Subject: Re: ECOH 20x20 OH1 Obstructed Construction

*3.7.1* Obstructed Construction. *Panel construction and other

construction where beams, trusses, or other members impede

heat flow or water distribution in a manner that materially affects
the ability of sprinklers to control or suppress a fire.

*A.3.7.1 Obstructed Construction. *The following are examples

of obstructed construction. The definitions are provided to assist

the user in determining the type of construction feature.

(1) *Beam and Girder Construction*. The term *beam and girder construction*

as used in this standard includes noncombustible

and combustible roof or floor decks supported by wood

beams of 4 in. (102 mm) or greater nominal thickness or

concrete or steel beams spaced 3 ft to 71/2 ft (0.9mto 2.3 m)

on center and either supported on or framed into girders.

[Where supporting a wood plank deck, this includes semimill

and panel construction, and where supporting (with

steel framing) gypsum plank, steel deck, concrete, tile, or

similar material, this includes much of the so-called noncombustible

construction.]



*8.8.4.1.2 Obstructed Construction. *Under obstructed construction,

the sprinkler deflector shall be located in accordance

with one of the following arrangements:

(3) Installed in each bay of obstructed construction, with the

deflectors located a minimum of 1 in. (25.4 mm) and a

maximum of 12 in. (305 mm) below the ceiling.


R/

Matt