Not the selection, but the description. In  (#3) you are allowed 1-12. Not
the four listed,especially the 24"
Also, as you model proves, the affect of jet cooling out-weighs the
spraying of a couch, The 60gpm will make that moot as well..

R/
Matt


On Tue, Jul 15, 2014 at 11:05 AM, Brad Casterline <[email protected]>
wrote:

> Hmm Matt, I used (1), but then raised it to 3" above the bottom of beam in
> accordance with Table 8.8.5.1.2. (2007)
> Is that a mistake?
>
> Brad
>
> -----Original Message-----
> From: Matthew Willis [mailto:[email protected]]
> Sent: Tuesday, July 15, 2014 9:33 AM
> To: [email protected]
> Subject: Re: ECOH 20x20 OH1 Obstructed Construction
>
> *3.7.1* Obstructed Construction. *Panel construction and other
>
> construction where beams, trusses, or other members impede
>
> heat flow or water distribution in a manner that materially affects
> the ability of sprinklers to control or suppress a fire.
>
> *A.3.7.1 Obstructed Construction. *The following are examples
>
> of obstructed construction. The definitions are provided to assist
>
> the user in determining the type of construction feature.
>
> (1) *Beam and Girder Construction*. The term *beam and girder construction*
>
> as used in this standard includes noncombustible
>
> and combustible roof or floor decks supported by wood
>
> beams of 4 in. (102 mm) or greater nominal thickness or
>
> concrete or steel beams spaced 3 ft to 71/2 ft (0.9mto 2.3 m)
>
> on center and either supported on or framed into girders.
>
> [Where supporting a wood plank deck, this includes semimill
>
> and panel construction, and where supporting (with
>
> steel framing) gypsum plank, steel deck, concrete, tile, or
>
> similar material, this includes much of the so-called noncombustible
>
> construction.]
>
>
>
> *8.8.4.1.2 Obstructed Construction. *Under obstructed construction,
>
> the sprinkler deflector shall be located in accordance
>
> with one of the following arrangements:
>
> (3) Installed in each bay of obstructed construction, with the
>
> deflectors located a minimum of 1 in. (25.4 mm) and a
>
> maximum of 12 in. (305 mm) below the ceiling.
>
>
> R/
>
> Matt
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to