Sometimes that's what it takes, success often involves some level of
negotiation.

John

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Friday, July 18, 2014 10:19 PM
To: [email protected]
Subject: Re: Segue to AHJ's from CPVC Underground

You're alright like most of us the psychology part of sprinkler work just
makes you want to throw up in your mouth a little bit ,  right?

> On Jul 18, 2014, at 9:09 PM, <[email protected]> wrote:
> 
> How about everything is per code except we have two pumps rather than
one.and we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most
ignorant thing I have ever seen. Just found out the chief told plan reviewer
no more written correspondence. I guess because they don't want a written
orecord of their stupidity. Please forgive my frustration but I just don't
know where to go from here.. 
> 
> Ron fletcher Sent from my iPhone
> 
>> On Jul 18, 2014, at 4:24 PM, "John Drucker - Home"
<[email protected]> wrote:
>> 
>> Ron, et.al.
>> 
>> I don't know the particulars of your situation but we have a saying; 
>> there's your side, their side and the truth.  Perhaps there's an 
>> issue with the code itself,  a local amendment or interpretation. 
>> There's got to be something driving this.
>> 
>> Case in point about a reference standard, NFPA-72 speaks of wall 
>> mounted smoke detectors/alarms and calls out a distance yet the 
>> illustration in the annex is worded differently than the code.
>> 
>> 29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on 
>> walls shall be located NOT FARTHER than 12 in. (300 mm) from the 
>> adjoining ceiling surface.
>> 
>> Yet the annex A.29.8.3 notes;  "Measurements shown are to the closest 
>> edge of the detector".
>> 
>> According to the annex this would place part or most of the alarm or 
>> detector FARTHER than 12 in. from the adjoining ceiling surface.
>> 
>> It's important to note that Annex A opens with the following 
>> statement;
>> 
>> "Annex A is not a part of the requirements of this NFPA document but 
>> is included for informational purposes only. This annex contains 
>> explanatory material, numbered to correspond with the applicable text
paragraphs"
>> 
>> Yet when brought to NFPA's attention the answer from the NFPA 
>> representative was interpreted from the Annex material.  This is 
>> clearly incorrect, the annex and the illustration are not part of the
code.  In either case fix the
>> code language or the annex.   The same happens in I Code Commentaries and
>> various subject matter books that often interpret, amend or 
>> supplement the actual code language.  In a nutshell our codes and 
>> standards have become a maze of requirements, exceptions and 
>> interpretations.  This should be a warning flag to the code 
>> community.  Perhaps the code official has just reached his limit and 
>> is instead relying on empirical experience in the face of confusion.
>> 
>> I have situation at this very moment on two different projects that 
>> impose an operational issue for the fire department, one that the 
>> code is not considering.  However my approach is to get everyone 
>> around the table do some brainstorming and come up with an equitable
technical solution.
>> Perhaps by finding the root cause of your situation the stakeholders will
>> put down their swords and solve the problem.   Food for thought.
>> 
>> Best wishes, always available should the need arise.
>> 
>> Sincerely,
>> 
>> John
>> 
>> John Drucker, CET
>> Assistant Construction Official
>> Fire Protection Subcode Official
>> Building/Fire/Electrical Inspector
>> Borough of Red Bank
>> Red Bank, New Jersey
>> Email: [email protected]
>> Cell/Text: 732-904-6823
>> 
>> Safe Buildings Save Lives !
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum 
>> [mailto:[email protected]]
>> On Behalf Of [email protected]
>> Sent: Friday, July 18, 2014 1:04 PM
>> To: [email protected]
>> Subject: Segue to AHJ's from CPVC Underground
>> 
>> It's Friday so I figured I'd whine on the forum.  To set the stage, 
>> prior to the letter I am referring to we had approved permitted 
>> drawings from the AHJ. The following is a quote from a letter we received
from that same AHJ.
>> 
>> "At this time , Blah Blah Blah Fire Protection District is denying 
>> said plans and is requesting a re-submittal of new plans that exceed 
>> IFC, UFC, and NFPA standards." Nowhere in the body of the letter does 
>> he say exactly how we are to "EXCEED" IFC, UFC and NFPA. In the 
>> letter they basically outline that what was submitted meets the all 
>> of the codes. I was told by the author of the letter at a meeting the 
>> day before that he didn't care what the code said because he is the 
>> AHJ and per Section 104 of the IFC he can make us do whatever he 
>> wants. Then he said "do it my way or there will be no Certificate of 
>> Occupancy."  We are 4-5 weeks away from a CofO and the change 
>> involves increasing the size of two new diesel pumps that are being 
>> installed. The fire chief told us to go to the State Fire Marshal if we
wanted to appeal. I'm a bit frustrated with AHJ's right now.
>> 
>> Ron F
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to