Lo and Behold you can use ESFR with solid shelving.  Historically that was 
explicitly forbidden.  Then in 2013 the technical committee said well actually 
it is forbidden for ALL sprinkler types but we’ve allowed it for a long time 
for spray sprinklers provided the solid shelf criteria in 16.1.6 / 17.1.5 is 
concurrently applied.  So why not allow it for ESFR and CMSA too.  It was 
intended to be applied through but it actually appeared only in 16.2.3.2 (up to 
25 ft Class I-IV) and 17.3.3.1.1 (>25 ft Group A plastics).  Again the Solid 
shelf criteria of 16.1.6 and 17.1.5 must be concurrently applied.  For the next 
addition, it was recognized that we did not provide said guidance for all 
sprinkler types so it was added throughout including CMSA.  One difference is 
that for spray sprinklers, in-racks must be provided below all solid shelves 
but not those that are open (in a vertical arrangement where they differ) but 
for CXMSA and ESFR all tiers beneath the upper most solid shelf must have 
in-racks. This was not stated in the 2013 edition.  Note that this has not 
completed the cycle (Correlating committee must still meet was well as the 
Technical Session at the convention).  None the less, the 2013 ed clearly shows 
it is on its way for CMSA and ESFR.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 13, 2014, at 8:38 AM, Richard Mote <[email protected]> wrote:

> Here is the scenario;
> 
> New  warehouse addition to an existing sprinklered automotive parts 
> distribution warehouse.
> Peak height = 36'-1", Rack height = 28'.
> Addition was originally specified for an ESFR system with racks. They came 
> back and said they wanted to be able to store small quantities of flammable 
> liquids. The insurance reviewer said OK add 1 level of in rack sprinkler 
> where the flammable liquid  storage would be. The customer said, we don't 
> know it may move around depending on how much we have at any given time, so 
> install sprinkler in all the racks. Yesterday I get the final rack layout 
> drawings which call for solid steel shelving at the 12' and 28' levels. I 
> responded that per NFPA 13, 2007 (the current recognized addition in PA) 
> 16.3.3.2 you can't use ESFR with solid shelving.  Now the customer wants to 
> know. If we install in-racks at the 27' and 11' levels could we still use 
> ESFR at the roof? (sort of defeats the purpose but it's not my money)I have 
> spent the last hour going through chapters 16 & 17. I can't find anything 
> that say you could do that. But I also haven't found anything that says you 
> can't other than 16
> .3.3.2 & 17.2.3.1.1. At this point I want to hang my hat on that and say no 
> we can't. However I may be missing something so I thought I would throw it 
> out for discussion.
> 
> Richard Mote ET
> Design Manager
> Rowe Sprinkler Systems, Inc.
> PO Box 407
> Middleburg, PA 17842
> P- 877-324-ROWE
> F- 570-937-6335
> [email protected]<mailto:[email protected]>
> www.rowesprinkler.com<http://www.rowesprinkler.com/>
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to