The reason for requiring QR is that we intend to protect a ceiling with 14 inch pockets. So we follow 8.6.7.2.(6) NFPA 13 ed 2013 that requires QR, and the exception for sprinklers in each pocket.
I got the reply from Tyco, the SW 20 and SW 24 are only available in standard response. -----Mensaje original----- De: Sprinklerforum [mailto:[email protected]] En nombre de ampeck Enviado el: miércoles, 20 de agosto de 2014 05:24 a.m. Para: [email protected] Asunto: Re: Sidewall sprinkler EC QR listed for ordinary hazard II That or 8.3.3.2 Where quick response sprinklers are installed, ALL sprinkler within a compartment shall be quick response. I doubt its for QR reduction if its a pocket ceiling? Dont know what kind of pockets but probably have unprotected pockets greater the 32 sq ft. Im just guessing. I have no idea about a EC QR OHII HSW, the closest thing I can find is TYCO EC-HS-8.0 and it says installation per VdS CEA 4001, Annex E, LH/OHI. Nothing about OHII. On Aug 20, 2014, at 1:49 PM, Brad Casterline <[email protected]> wrote: > QR Reduction? > >> On Aug 20, 2014, at 1:37 AM, Aaron Peck <[email protected]> wrote: >> >> Maybe because there's existing sprinklers that stay and are quick response? Only reason I can think of. >> >> Aaron M. Peck SET >> +1 (202) 407-9079 Skype >> +855 (78) 700-407 >> Sent from my iPad >> >>> On Aug 20, 2014, at 3:44 AM, John O'Connor <[email protected]> wrote: >>> >>> Tyco makes the SW-20 and SW-24 for OH. It's Extended coverage, >>> K=11.2 in Standard Response. You can use S/R in Ord Hazard. Why >>> the need for QR in an OH occupancy? >>> John O'Connor >>> >>> -----Original Message----- >>> From: Sprinklerforum >>> [mailto:[email protected]] >>> On Behalf Of J.P. Merlino/Ing. L.Lagomarsino & Asoc. >>> Sent: Tuesday, August 19, 2014 2:48 PM >>> To: [email protected] >>> Subject: Sidewall sprinkler EC QR listed for ordinary hazard II >>> >>> Dear sirs: >>> >>> Is there any sidewall sprinkler with extended coverage, listed for >>> ordinary hazard II and quick response? >>> >>> We need to protect an existing mercantile occupancy with a low >>> height pocket ceiling. >>> >>> regards >>> >>> J.P. Merlino >>> >>> >>> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin >>> kler.org >>> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin >>> kler.org >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink >> ler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ----- No se encontraron virus en este mensaje. Comprobado por AVG - www.avg.com Versión: 2013.0.3485 / Base de datos de virus: 3955/8069 - Fecha de publicación: 08/20/14 ----- No se encontraron virus en este mensaje. Comprobado por AVG - www.avg.com Versión: 2013.0.3485 / Base de datos de virus: 3955/8069 - Fecha de publicación: 08/20/14 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org