That is mind-bending Craig, thanks. I do not doubt the procedure for coming
up with 2 million. I guess what's bothering me is along these lines: "If a
couple three thousand GPM flowing for 30 minutes doesn't do the trick, how
is 10 times that going to help"?

Brad

-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Thursday, August 28, 2014 7:11 AM
To: [email protected]
Subject: RE: 1, 2 & 3 hour stored water duration requirements

Fire Flow from Section 507 of the IFC is typically the driver when it comes
to large aboveground tanks.  This is one issue often forgotten or overlooked
in fire protection design.  

When determining the adequacy of water supplies, both the sprinkler flow and
Fire Flow must be considered.  

I had a project last year with 8000 gpm for 4 hour duration for fire flow.
Yes it was a big honking tank, 2 million gallons.   Deluge system flows were
at the 7500 gpm mark.  

Got one right now that's a bit smaller with only 6000 gpm for 4 hours for
fire flow.  

Rule of thumb for estimating tank cost is between .60 cents and $1.00 a
gallon depending on location and installation issues.