The Fire Flow value is not about sprinklers.  It is about hydrant flow.  
Remember the majority of sprinklers are designed to control, (suppression mode 
aside) not necessarily extinguish the fire.  So in a significant fire, the fire 
department is tasked with the extinguishing effort via hydrants and manual hose 
lines.   

Depending on the conditions of the fire, the manual fire fight could take 
hours.  Recent warehouse fire was a 13 hour fire fight due to the commodity.  
So if you flow 1000-1500 from a deck gun then add 3-4 hose lines at 250 -500 
gpm each and you can see where a lot of water can be used rather quickly.

Remember that for the most part sprinkler flow is 1 hour or 2 hours, not 4 
hours.  

I think as fire protection engineers/designers we primarily focus on the 
sprinklers and often forget that when the sprinklers go off, that's only the 
beginning of the suppression effort.  There is much more tied into this work we 
do.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Thursday, August 28, 2014 9:09 AM
To: [email protected]
Subject: RE: 1, 2 & 3 hour stored water duration requirements

That is mind-bending Craig, thanks. I do not doubt the procedure for coming up 
with 2 million. I guess what's bothering me is along these lines: "If a couple 
three thousand GPM flowing for 30 minutes doesn't do the trick, how is 10 times 
that going to help"?

Brad

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Thursday, August 28, 2014 7:11 AM
To: [email protected]
Subject: RE: 1, 2 & 3 hour stored water duration requirements

Fire Flow from Section 507 of the IFC is typically the driver when it comes to 
large aboveground tanks.  This is one issue often forgotten or overlooked in 
fire protection design.  

When determining the adequacy of water supplies, both the sprinkler flow and 
Fire Flow must be considered.  

I had a project last year with 8000 gpm for 4 hour duration for fire flow.
Yes it was a big honking tank, 2 million gallons.   Deluge system flows were
at the 7500 gpm mark.  

Got one right now that's a bit smaller with only 6000 gpm for 4 hours for fire 
flow.  

Rule of thumb for estimating tank cost is between .60 cents and $1.00 a gallon 
depending on location and installation issues.



Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to