Thanks for that link, I think many of us could use a refresher. Myself 
especially, I haven’t done much and my last seismic class was back in 2009 and 
the amount of seismic calculations I’ve done since then is less than I can 
count on one hand.

On Sep 5, 2014, at 11:10 PM, Jack Carlson <[email protected]> wrote:

> This is the link to the Sept 10th webinar...
> 
> http://www.firesprinkler.org/training/webinars/20140910.html
> 
> 
> Jack W. Carlson, SET
> Triple "A" Fire Protection
> Office - 251.649.2034
> Fax - 251.649.2037
> Cell - 706.247.5050
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of [email protected]
> Sent: Friday, September 05, 2014 11:58 AM
> To: sprinklerforum
> Subject: Re: Seismic bracing
> 
> 
> 
> Oh boy, here we go again.  Every time the subject of seismic bracing / 
> protection comes up, it shows that there is a general lack of understanding 
> among contractors and designers (myself included) as to when it is required, 
> what is required, and how to do it correctly. 
> We need more education - just reading NFPA13 is not enough.  Can anyone 
> suggest any good classes available out there? 
> 
> Thanks 
> 
> Bill Menster 
> 
> ----- Original Message -----
> 
> From: [email protected]
> To: "sprinklerforum" <[email protected]>
> Sent: Friday, September 5, 2014 11:10:38 AM
> Subject: RE: Seismic bracing 
> 
> Some jurisdictions around here require what we call "feel good bracing". They 
> don't require calculations, or that the building be designed to any seismic 
> standard, they just want the minimum bracing. If we want a green tag we have 
> to put it in. I guess in this case the question would be if the only 
> requirement is local dictate can you install at the max spacing and not do 
> any calc's provided it is acceptable to the AHJ? Ron F 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Parsley Consulting
> Sent: Friday, September 05, 2014 5:11 AM
> To: [email protected]
> Subject: Re: Seismic bracing 
> 
> Stephen,
>      I don't believe the AHJ you're dealing with has thought this decision 
> through very carefully.  They seem to be equating "seismic bracing" with 
> "seismic protection", which includes such other features as flexible 
> couplings, clearance requirements, seismic separation assemblies, restraint 
> of branch lines, and certain hanger requirements in a building protected 
> against seismic damage.  Section 9.3 covers more than just seismic bracing. 
>      I would recommend you ask the AHJ if they're going to require all of the 
> features in NFPA 13 for seismic protection, or just lateral, longitudinal and 
> riser bracing. 
>      It's also relevant to note that if you're going to provide seismic 
> bracing you have to make sure you comply with 9.3.5.1.2 (2007), which 
> requires the structure to be able to withstand the applied seismic loads.  
> Based on what you've described I would wager a few dollars that they could 
> not do so. 
>      And, if you still have a mandate to brace, ask the AHJ to provide the Ss 
> value for the building, per 9.3.5.6.2. 
>      Craig Prahl is correct, in that a requirement for seismic protection of 
> a building is based on the location of the building in a seismic zone, and 
> it's occupancy or use.  While it isn't a complicated set of data to find and 
> apply correctly, you're not a structural or soils engineer, and that is 
> certainly not your responsibility. 
>      This is a bad idea without something more to back it up.  You did 
> mention that the building code requires it, can you be more specific? 
> *Ken Wagoner, SET*
> **Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, California 92025
> *****Phone 760-745-6181*
> Visit our website <http://www.parsleyconsulting.com/> *** On 9/5/2014 8:31 
> AM, Steve Sorrell wrote: 
>> Sorry,  should have read 2007 edition
>> 
>> Stephen J. Sorrell, CET
>> NICET# 77901 Level III
>> E mail: [email protected]
>> 
>> Performance Fire Protection, LLC
>> Corporate Office
>> 179 Gasoline Alley -  PO Box 4510
>> Mooresville, NC 28117
>> Phone: 704-663-1664  Fax: 704-663-1652 Cell : 704-309-1242
>> 
>> Web: www.performancefire.com
>> Licensed in NC, SC, VA, TN, GA, AL
>> 
>> "Performance on Every Level." 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]] On Behalf Of 
>> [email protected]
>> Sent: Friday, September 05, 2014 8:33 AM
>> To: [email protected]
>> Subject: RE: Seismic bracing
>> 
>> The AHJ can't just "require it".  His preference is not relevant.  Also 
>> seismic bracing is not based on Zones or Maps anymore, hasn't been for quite 
>> a while. 
>> 
>> I'm curious why you're using the 2000 edition of NFPA 13. 
>> 
>> Anyway back to seismic. 
>> 
>> Seismic requirements are determined based on a number of factors originating 
>> out of the Building Code Chapter 16.  It's not just an arbitrary decision. 
>> 
>> There needs to be a geotech (soils) report, the building needs to be 
>> classified as to its use/function and you go from there. 
>> 
>> So there are engineering questions to be answered before there a requirement 
>> for bracing is established. 
>> 
>> I've had to provide bracing on new work in an existing building, it made no 
>> sense since the building structure wasn't design for the loading and the 
>> rest of the system was not protected but it was required by the code so it 
>> had to be done.  Was it required on the original install, did someone just 
>> miss it assuming the site wasn't in "the zone", who knows. 
>> 
>> There is a lot of misinterpretation on the part of design professionals 
>> regard when it's required and when it's not. 
>> 
>> Craig L. Prahl
>> Fire Protection Group Lead
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> Spartanburg, SC  29303
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> CH2MHILL Extension  74102
>> [email protected]
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]] On Behalf Of 
>> Steve Sorrell
>> Sent: Friday, September 05, 2014 8:13 AM
>> To: [email protected]
>> Subject: Seismic bracing
>> 
>> I need some help with a seismic problem. 
>> I am making modifications to a 1970's sprinkler system in NC, we are using 
>> the 2000 ed of NFPA  13. 
>> There is no seismic bracing on this system. 
>> I have had to add some new main in various areas. 
>> The local AHJ is requiring that only the new sprinkler main will need to be 
>> braced. 
>> Does anyone know if this is an actual standards requirement or just a 
>> preference of the local AHJ ? 
>> Obviously I am trying to avoid installing the seismic bracing on this 
>> project. 
>> 
>> 
>> Stephen J. Sorrell, CET
>> NICET# 77901 Level III
>> E mail: 
>> [email protected]<mailto:[email protected]>
>> 
>> Performance Fire Protection, LLC
>> Corporate Office
>> 179 Gasoline Alley -  PO Box 4510
>> Mooresville, NC 28117
>> Phone: 704-663-1664  Fax: 704-663-1652 Cell : 704-309-1242
>> 
>> Web: www.performancefire.com<http://www.performancefire.com>
>> Licensed in NC, SC, VA, TN, GA, AL
>> 
>> "Performance on Every Level." 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>> 
>> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to