Since it is an existing building I doubt any of the things you have listed will be done. I guess I look at getting it done without doing any harm so the owner can use the building. The alternative appears to be telling the owner it's not their responsibility and that he has to get an architect, structural engineer, soils report and have as builts done for the whole building and so on and so on so that the sprinkler contractor can properly design a sway brace. Ron F
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jim Davidson Sent: Friday, September 05, 2014 9:28 AM To: [email protected] Subject: RE: Seismic bracing The seismic design classification should be determined by the structural engineer who determines the SDC of the site. Once the SDC is determined then you can go into either, ASCE 7 or Chapter 16 of the IBC, to determine the building's importance factor and other determining factors to decide when earthquake bracing is required. For example in most cases a building has a SDC of C then the mechanical and electrical systems with an importance factor of less than 1.5 do not have to seismically brace the systems however systems with an importance factor equal to or greater than 1.5 (fire alarm, sprinkler, fire pump, stair tower pressurization, etc) are required to be seismically braced. Then you can go to NFPA 13 or the IBC for the details on bracing and the zone of influence calculations required. Because of the soil and underground geological analysis the structural engineer will need to determine the SDC of the site. Regards Jim DAVIDSON ASSOCIATES Fire Protection Engineering P. O. Box 4002 Code Consultants Greenville, DE 19807 (302) 994-9500 Fax (302) 994-3414 CONFIDENTIALITY This report and any attachments are confidential and also may be privileged. If you are not the named recipient, or have otherwise received this report in error, please destroy the report, notify the sender immediately, and do not disclose its contents to any other person, use them for any purpose, or store or copy them in any medium. Thank you for your cooperation. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Friday, September 05, 2014 12:16 PM To: sprinklerforum Subject: Re: Seismic bracing Oh boy, here we go again. Every time the subject of seismic bracing / protection comes up, it shows that there is a general lack of understanding among contractors and designers (myself included) as to when it is required, what is required, and how to do it correctly. We need more education - just reading NFPA13 is not enough. Can anyone suggest any good classes available out there? Thanks Bill Menster ----- Original Message ----- From: [email protected] To: "sprinklerforum" <[email protected]> Sent: Friday, September 5, 2014 11:10:38 AM Subject: RE: Seismic bracing Some jurisdictions around here require what we call "feel good bracing". They don't require calculations, or that the building be designed to any seismic standard, they just want the minimum bracing. If we want a green tag we have to put it in. I guess in this case the question would be if the only requirement is local dictate can you install at the max spacing and not do any calc's provided it is acceptable to the AHJ? Ron F -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Parsley Consulting Sent: Friday, September 05, 2014 5:11 AM To: [email protected] Subject: Re: Seismic bracing Stephen, I don't believe the AHJ you're dealing with has thought this decision through very carefully. They seem to be equating "seismic bracing" with "seismic protection", which includes such other features as flexible couplings, clearance requirements, seismic separation assemblies, restraint of branch lines, and certain hanger requirements in a building protected against seismic damage. Section 9.3 covers more than just seismic bracing. I would recommend you ask the AHJ if they're going to require all of the features in NFPA 13 for seismic protection, or just lateral, longitudinal and riser bracing. It's also relevant to note that if you're going to provide seismic bracing you have to make sure you comply with 9.3.5.1.2 (2007), which requires the structure to be able to withstand the applied seismic loads. Based on what you've described I would wager a few dollars that they could not do so. And, if you still have a mandate to brace, ask the AHJ to provide the Ss value for the building, per 9.3.5.6.2. Craig Prahl is correct, in that a requirement for seismic protection of a building is based on the location of the building in a seismic zone, and it's occupancy or use. While it isn't a complicated set of data to find and apply correctly, you're not a structural or soils engineer, and that is certainly not your responsibility. This is a bad idea without something more to back it up. You did mention that the building code requires it, can you be more specific? *Ken Wagoner, SET* **Parsley Consulting*** *350 West 9th Avenue, Suite 206 *Escondido, California 92025 *****Phone 760-745-6181* Visit our website <http://www.parsleyconsulting.com/> *** On 9/5/2014 8:31 AM, Steve Sorrell wrote: > Sorry, should have read 2007 edition > > Stephen J. Sorrell, CET > NICET# 77901 Level III > E mail: [email protected] > > Performance Fire Protection, LLC > Corporate Office > 179 Gasoline Alley - PO Box 4510 > Mooresville, NC 28117 > Phone: 704-663-1664 Fax: 704-663-1652 Cell : 704-309-1242 > > Web: www.performancefire.com > Licensed in NC, SC, VA, TN, GA, AL > > "Performance on Every Level." > > > -----Original Message----- > From: Sprinklerforum > [mailto:[email protected]] On Behalf Of > [email protected] > Sent: Friday, September 05, 2014 8:33 AM > To: [email protected] > Subject: RE: Seismic bracing > > The AHJ can't just "require it". His preference is not relevant. Also > seismic bracing is not based on Zones or Maps anymore, hasn't been for quite > a while. > > I'm curious why you're using the 2000 edition of NFPA 13. > > Anyway back to seismic. > > Seismic requirements are determined based on a number of factors originating > out of the Building Code Chapter 16. It's not just an arbitrary decision. > > There needs to be a geotech (soils) report, the building needs to be > classified as to its use/function and you go from there. > > So there are engineering questions to be answered before there a requirement > for bracing is established. > > I've had to provide bracing on new work in an existing building, it made no > sense since the building structure wasn't design for the loading and the rest > of the system was not protected but it was required by the code so it had to > be done. Was it required on the original install, did someone just miss it > assuming the site wasn't in "the zone", who knows. > > There is a lot of misinterpretation on the part of design professionals > regard when it's required and when it's not. > > Craig L. Prahl > Fire Protection Group Lead > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29303 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > > -----Original Message----- > From: Sprinklerforum > [mailto:[email protected]] On Behalf Of > Steve Sorrell > Sent: Friday, September 05, 2014 8:13 AM > To: [email protected] > Subject: Seismic bracing > > I need some help with a seismic problem. > I am making modifications to a 1970's sprinkler system in NC, we are using > the 2000 ed of NFPA 13. > There is no seismic bracing on this system. > I have had to add some new main in various areas. > The local AHJ is requiring that only the new sprinkler main will need to be > braced. > Does anyone know if this is an actual standards requirement or just a > preference of the local AHJ ? > Obviously I am trying to avoid installing the seismic bracing on this > project. > > > Stephen J. Sorrell, CET > NICET# 77901 Level III > E mail: > [email protected]<mailto:[email protected]> > > Performance Fire Protection, LLC > Corporate Office > 179 Gasoline Alley - PO Box 4510 > Mooresville, NC 28117 > Phone: 704-663-1664 Fax: 704-663-1652 Cell : 704-309-1242 > > Web: www.performancefire.com<http://www.performancefire.com> > Licensed in NC, SC, VA, TN, GA, AL > > "Performance on Every Level." > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org