I have been asked to extend sprinkler coverage to an addition, 17.5’ long x 13’ 
across.  The ceiling is a cathedral ceiling, 13’ 2” at the ceiling and 9’ 3 “ 
high at the sidewall.  The existing sprinkler piping is behind the 13’ wall, 
pointing down the 17.5’ length.  No body can find plans from the original 
construction, there is not a hydraulic nameplate on the sprinkler system.  The 
Fire Chief remembers that during construction, the water supply was 
“questionable”.    There is not a forward flow port so  I can not get a water 
GPM/psi measurement.  There is a 1.5 “ FDC at the front of the building. There 
is a fire hydrant across the parking lot, about 75 feet away.  The 5 year 
average for the static pressure is 34 psi and the residual is 27 psi, through 
the main drain.  

The building is about 13 years old and is a retirement home.  

My concern is the lack of information about the water supply.  The building is 
on a hill, about the level of the municipal water tank, which is on another 
hill.   

Can I get an accurate reading on the water supply from the fire hydrant, or the 
2” main drain?  Or should I put a Forward Flow test port in before doing 
anything else?  And if I do get a good water reading, I still will not know 
what the system demand is.  So then do I need to hire someone to crawl the 
attic and take measurements of the piping?  

 


   