Doesn't the AHJ tell you what you need to submit for a permit?
You'll have to calculate the addition.
Also, you can't get an accurate measurement of water supply from the 2" main drain. There have been formula's out there with different methods but they are not accepted as true.


On 11/5/2014 4:16 PM, Douglas Hicks wrote:
I have been asked to extend sprinkler coverage to an addition, 17.5’ long x 13’ 
across.  The ceiling is a cathedral ceiling, 13’ 2” at the ceiling and 9’ 3 “ 
high at the sidewall.  The existing sprinkler piping is behind the 13’ wall, 
pointing down the 17.5’ length.  No body can find plans from the original 
construction, there is not a hydraulic nameplate on the sprinkler system.  The 
Fire Chief remembers that during construction, the water supply was 
“questionable”.    There is not a forward flow port so  I can not get a water 
GPM/psi measurement.  There is a 1.5 “ FDC at the front of the building. There 
is a fire hydrant across the parking lot, about 75 feet away.  The 5 year 
average for the static pressure is 34 psi and the residual is 27 psi, through 
the main drain.

The building is about 13 years old and is a retirement home.

My concern is the lack of information about the water supply.  The building is 
on a hill, about the level of the municipal water tank, which is on another 
hill.

Can I get an accurate reading on the water supply from the fire hydrant, or the 
2” main drain?  Or should I put a Forward Flow test port in before doing 
anything else?  And if I do get a good water reading, I still will not know 
what the system demand is.  So then do I need to hire someone to crawl the 
attic and take measurements of the piping?


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


--
Forest Wilson
Project Manager
193 California St
Xenia OH 45385
Ph: 937-736-0425

///WHO IS JOHN GALT?///

******This email and any files transmitted with it are confidential and 
intended solely for the use of the individual or entity to whom they are 
addressed. If you have received this email in error please notify the system 
manager. This message contains confidential information and is intended only 
for the individual named. If you are not the named addressee you should not 
disseminate, distribute or copy this e-mail. Please notify the sender 
immediately by e-mail if you have received this e-mail by mistake and delete 
this e-mail from your system. If you are not the intended recipient you are 
notified that disclosing, copying, distributing or taking any action in 
reliance on the contents of this information is strictly prohibited.***

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to