Assuming it’s the same specs the UFC has recently changed to in the last year. 
FM design requirements for Ordinary hazard I are a big jump from NFPA. Not sure 
if it is a change from before not having don't one in while myself. But for a 
30'-0" of less ceiling building you need 0.20/2500 with 8.0K heads  and 250 
hose.  This is per FMG Engineering Bulletin 4-12. Maybe you'll different 
criteria. 

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Monday, November 10, 2014 8:27 AM
To: [email protected]
Subject: FM Global requirements

I have a project that may be switching to FM global requirements.  I haven’t 
worked with FM for a while so what are the main differences between NFPA 13 and 
FM?  The plans have already been approved by the AHJ so the owner is looking 
for any potential cost impact.  I know that the products used should be FM 
approved.  I did take a reduced design area for my light hazard areas.

Thanks,



Dewayne