Foam in generator rooms.

Jack Fairchild


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Todd - Work
Sent: Monday, November 10, 2014 5:16 PM
To: [email protected]
Subject: Re: FM Global requirements

What Craig said, but FM typically does not recognize QR sprinkler reductions.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Nov 10, 2014, at 11:40 AM, <[email protected]> <[email protected]> 
> wrote:
> 
> One thing that needs to be understood is that FM is not an AHJ, they make 
> recommendations not requirements.  
> 
> FM should provide a letter or review of the project and provide 
> recommendations to the owner.  Then the owner takes those recommendations and 
> tells you as the contractor which ones they want to consider.  It's not a 
> blanket set of requirements.  You should not have to determine which Data 
> Sheets to follow and which not and to what extent.  
> 
> I have had some clients that negotiate everything with the FM rep., others 
> take all the recommendations at 100% so your results may vary.
> 
> Also I have found that FM opinions and directions vary depending on which 
> office and which individuals you deal with.  
> 
> This is not a slam or criticism of any of the FM people I've dealt with over 
> the years.  Just an observation.
> 
> So you need to let the owner know there may be changes but he needs to get 
> with the FM rep, receive FM's recommendations and then the owner directs 
> which ones he wants you to employ.
> 
> Craig L. Prahl
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
> 
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Dewayne Martinez
> Sent: Monday, November 10, 2014 11:27 AM
> To: [email protected]
> Subject: FM Global requirements
> 
> I have a project that may be switching to FM global requirements.  I haven’t 
> worked with FM for a while so what are the main differences between NFPA 13 
> and FM?  The plans have already been approved by the AHJ so the owner is 
> looking for any potential cost impact.  I know that the products used should 
> be FM approved.  I did take a reduced design area for my light hazard areas.
> 
> Thanks,
> 
> 
> 
> Dewayne
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to