If you are referring to the requirements that ells and tees shall have their 
centerline perpendicular to the horizontal split case pump or if parallel be 
located 10 pipe diameters from the suction flange, then no you are not missing 
anything as vertical in-line pumps are not affected by the unbalanced, 
turbulent flow in the same way as horiz. split-case.

Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection Designer 
| Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Monday, November 24, 2014 9:09 AM
To: [email protected]
Subject: Vertical Inline Pump

NFPA-20 sets limitations on elbows & tee's with regard to horizontal split-case 
pumps, I don't see anything like that for vertical in-line pumps, am I missing 
something?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to