Horizontal split case have a double inlet to the impeller. It is important to keep each side balanced. Water turbulence that is parallel to the shaft creates an imbalance, hence the rules. Turbulence that is perpendicular to the shaft does not create the imbalance in loading the impeller. Vertical in-line pumps only have a single inlet, so water turbulence from these fittings/components does not affect the loading, hence no rules for the VIP.
Duane Johnson, PE Design Manager Strickland Fire Protection 301-474-1136 Office 301-455-0010 Cell -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Monday, November 24, 2014 10:09 AM To: [email protected] Subject: Vertical Inline Pump NFPA-20 sets limitations on elbows & tee's with regard to horizontal split-case pumps, I don't see anything like that for vertical in-line pumps, am I missing something? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org