Horizontal split case have a double inlet to the impeller. It is important to 
keep each side balanced. Water turbulence that is parallel to the shaft creates 
an imbalance, hence the rules. Turbulence that is perpendicular to the shaft 
does not create the imbalance in loading the impeller. Vertical in-line pumps 
only have a single inlet, so water turbulence from these fittings/components 
does not affect the loading, hence no rules for the VIP.

Duane Johnson, PE
Design Manager
Strickland Fire Protection
301-474-1136 Office
301-455-0010 Cell



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Monday, November 24, 2014 10:09 AM
To: [email protected]
Subject: Vertical Inline Pump

NFPA-20 sets limitations on elbows & tee's with regard to horizontal split-case 
pumps, I don't see anything like that for vertical in-line pumps, am I missing 
something?